Compressor wiring question - http://www.hvacmechanic.com/ Forums
Original message
| JBechtel | "Compressor wiring question" , posted Sat 19 Jun 07:58  
I have a Lennox hp20-311. Here's the deal. When I push the 208 relay in the compressor kicks in. I measured the voltage to the relay an instead of 24VAC i'm getting 4 VAC. If I disconnect the compressor from the interior unit I'm reading 24VAC on the Black, Blue, and Red lines relative to Green. Do I have a short somewhere?
Can somebody tell me where this short may be. I noticed the cool is off I'm still getting a reading of 6VAC on the Red relative to the Green. It seems to me they all should be 0?
| | Replies:
|
| Xenos Webmaster 
| "Re(1):Compressor wiring question" , posted Sat 19 Jun 16:54  
I think you have an open safety. Push in the red button on the small coper line.
Xenos.
The best way to escape a problem is to solve it.
|
|
|
|