"Heat pump Advice" , posted Sun 20 Jun 12:29:user profileedit/delete messagepost reply


I have a 400 square foot Glass Sunroom attached to my house that has a Friedrich 33,000 BTU Window Unit for AC. It is 10 Years old and is not very effecient with a EER of 9.0. I Live in Texas and the unit does not adequately cool the Sunroom. I am thinking of replacing with Trane XL 1600 Packaged Heat pump with SEER of 15.05 and nominal Tonnage of 5.

Do you think I will notice an improvement in Cooling and cost savings on Power Consumption?

Any suggestions will be appreciated.

Jeff Seabrook

http:/www.seabrook-services.com

[this message was edited by BUGSDOC1 on Sun 20 Jun 13:17]

 

Replies:

Xenos
Webmaster



64.230.160.88

"Re(1):Heat pump Advice" , posted Sun 20 Jun 13:51user profileedit/delete messagepost reply


Your room will be cooler however the costs will be higher, before you were only removing 3 tons now it's 5.

Xenos.

The best way to escape a problem is to solve it.

 

 

BUGSDOC1



4.14.166.225

"Re(2):Heat pump Advice" , posted Sun 20 Jun 14:26user profileedit/delete messagepost reply


Thanks for the response. Right now the 33000 unit does not cycle. It runs all day with the 90+ temps here in Texas. I was hoping to see the 60000 BTU unit at least cycle properly. Glass Rooms have an R-Value OF 0!!! We have installed cellular shades and they have had minimal impact on cooling demand.