"exhaust fan keeps running luxaire gas furnace" , posted Thu 21 Oct 23:26user profileedit/delete messagepost reply


good day, I have a luxaire gas furnace with a exhaust fan that wont shut off, I've tried cycling the thermostat, tapping the solenoid, hitting the side of the furnace,...Is there any usual suspect for this symptom? the furnace has continued to operate absolutely as usual, with the exception of the ever running exhaust fan...HELP>

 


Replies:

Mastertech



68.90.198.58

"Re(1):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 00:14user profileedit/delete messagepost reply


Exhaust fan may be a signal there something wrong. Check all the roll out switches(I think 3 in the burner section and maybe one in the blower section) Just push the button. Also the control board should give u a blinking code. Its near the blower.
Have u check the filter lately.

 

 

dmeskis

209.197.134.16

"Re(2):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 07:15user profileedit/delete messagepost reply


Ok, i'm a rank novice when it comes to furnaces, cars i know. What do the roll out switches look like? And how do i check them? I can't see any blinking light for a diagnostic code, is there a cover that may be hiding it? The filter is clean, it gets changed religiously every six years i mean months, seriously though it is almost new.

 

 

xenos
Webmaster



67.71.20.91

"Re(3):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 16:59user profileedit/delete messagepost reply


It's a temperature sensing switch located near the burners. and to test it just check it for continuity.

Xenos.

The best way to escape a problem is to solve it.

 

 

dmeskis

209.197.133.232

"Re(4):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 21:34user profileedit/delete messagepost reply


I think i found the sensor, two leads going into a small round thing bolted into the burner rail? If it is that there is continuity present while the exhaust fan is running. Is that correct?

don

 

 

xenos
Webmaster



67.71.20.91

"Re(5):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 22:23user profileedit/delete messagepost reply


That sounds correct, now you could have up to 3 ( normaly 2)limit devices and that is one .

Xenos.

The best way to escape a problem is to solve it.

 

 

dmeskis

209.197.133.229

"Re(6):exhaust fan keeps running luxaire gas f" , posted Fri 22 Oct 23:34user profileedit/delete messagepost reply


what are the other two? One i assume is the main control module? and the other? if there is another. The only other components that I can see, are the main control module, the vacuum switch, and a box with what looks like a capacitor or coil that is mounted to the side of the furnace with the main power wire going into it.

 

 

xenos
Webmaster



67.71.20.91

"Re(7):exhaust fan keeps running luxaire gas f" , posted Sat 23 Oct 19:09user profileedit/delete messagepost reply


One is normaly on the panel right in the center of the furnace and the last would be on the blower id the furnace is a downflow.

Xenos.