"bryant 383kav problems" , posted Fri 22 Oct 11:44user profileedit/delete messagepost reply


I have an upflow furnace made by bryant. When it gets the signal to heat, the hot surface ignitor glows and the gas valve opens. I see the flames but after about 3 seconds the valve shuts. I thought it was a bad flame sensor so I replaced it, but the problem remains. I try to jump the limit switch but I get 33 error. Any suggestions?

Thanks in advance.

 


Replies:

hvac_dude

63.117.227.232

"Re(1):bryant 383kav problems" , posted Fri 22 Oct 11:53user profileedit/delete messagepost reply


Check for any restiction in you exhaust pipe from your induced draft motor...