I have an upflow furnace made by bryant. When it gets the signal to heat, the hot surface ignitor glows and the gas valve opens. I see the flames but after about 3 seconds the valve shuts. I thought it was a bad flame sensor so I replaced it, but the problem remains. I try to jump the limit switch but I get 33 error. Any suggestions?
Thanks in advance.
Replies:
hvac_dude
"Re(1):bryant 383kav problems"
, posted Fri 22 Oct 11:53
Check for any restiction in you exhaust pipe from your induced draft motor...