ECM Motor & Module troubleshooting - http://www.hvacmechanic.com/ Forums
Original message
| Medcruise | "ECM Motor & Module troubleshooting" , posted Fri 22 Oct 21:49:  
I looked at a Carrier furnace (model 58sxBo8o-131GG). The inducer motor starts and the furnace fires but trips the limit switch due to the blower not starting. The owner stated that the motor & module were replaced two years ago.Its a G.E. module ( cno201ak6 ). I have 120 volts at the four pin harness.Also have voltage on the 16 pin harness. Is there an easy way to check this type of motor & module? The owner does not have manuals. thank you P.S. The motor turns freely and the module circuit board is not burnt or melted.
FISH ON!!
[this message was edited by Medcruise on Fri 22 Oct 22:14] | | Replies:
|
| xenos Webmaster 
| "Re(1):ECM Motor & Module troubleshooting" , posted Fri 22 Oct 22:28  
Acording to the information I have the 58Sx has just a standard 120 vac blower.
Xenos.
The best way to escape a problem is to solve it.
|
| | Medcruise | "Re(2):ECM Motor & Module troubleshooting" , posted Fri 22 Oct 22:51  
This is not a standard 120v blower. Furnace is 15 years old. Have you worked with ECM Motors. This is my first. Just looking for more info.Do you know of a tech support # for carrier? Thank you
FISH ON!!
|
| | Mastertech 
| "Re(3):ECM Motor & Module troubleshooting" , posted Sat 23 Oct 00:09  
Go here www.hvactechsupport.com/Dwnlds/Car-Bry_Lit/2stg8025Furn.pdf May not be the exact model but the guts are all the same.
|
|
|
|  |
|