Ultra SX 80 exhaust fan cycles over and over? - http://www.hvacmechanic.com/ Forums
Original message
| TimB | "Ultra SX 80 exhaust fan cycles over and over?" , posted Sat 23 Oct 15:04:  
We have an Armstrong Ultra SX 80 furnace. The furnace runs fine when heating...but when it is not heating the exhaust fan turns on and runs for about 5 seconds then shuts off and turns on again, over and over. The exhaust fan The problem started on its own...same programmable thermostat,no one has serviced it lately. I vacuumed it out and could see nothing visually wrong. Any idea what might be the problem? Thanks.
[this message was edited by TimB on Sun 24 Oct 12:46] | | Replies:
|
| xenos Webmaster 
| "Re(1):Ultra SX 80 exhaust fan cycles over and" , posted Sat 23 Oct 19:30  
With this discription almost anything.
Xenos.
The best way to escape a problem is to solve it.
|
| | Freon | "Re(2):Ultra SX 80 exhaust fan cycles over and" , posted Sun 24 Oct 14:57  
You might check the setting of the low temperature blower turn-off switch. Possibly it's set just low enough to cause this type of oscillation. If your furnace is old, this switch is most likely in a 3X5 aluminum box near to the control box but toward the end of the furnace where the air exits. Remove the cover and you'll see a dial and 3 sliders. The low temp slider should be the one positioned most clockwise-- at the low end of the temperature scale on the circular dial.
|
|
|
|  |
|