Furnace Woes - http://www.hvacmechanic.com/ Forums
Original message
| helpinde | "Furnace Woes" , posted Sun 24 Oct 16:26  
I have a Lennox Pulse 21 Furnace, Model G2104/5-100-3 (approx 11 years old). I posted a message 16 June 04 regarding heating and AC problems. AC response was right on and had a cool summer. Thanks.
I replaced previously the spark plug. Now with the chill in the air, I ordered a replacement ignition control circuit board 60J00. I replaced it as well as the wires that go to the spark plug and ignitor. Unfotunately, I still have no heat.
When the thermostat is set to come on, a motor would sound as if it was coming on. The unit gets hot but the blower never comes on and the limit control trips. If I set the thermostat to on, the blower does come on.
Any recommendations would be most appreciated.
| | Replies:
|
| xenos Webmaster 
| "Re(1):Furnace Woes" , posted Sun 24 Oct 23:07  
Look on the blower control board. What are the led’s doing?
Xenos.
The best way to escape a problem is to solve it.
|
|
|
|