I just replaced the thermostat for my Trane XE 1000 heat pump system and now nothing works. Called a tech to double check wire configuration and it was right. Inside blower/ outside unit/ AC/ Heat not energizing. What happened? Is there a reset on the unit outside or is there something I need to do to reset the starting circuitry? I was careful when switching thermostats but if wires touched or shorted would it mean re-wiring may be in order? (trane heat pump, rheem inside fan, honeywell thermostat) how much different does this make the wiring?

[this message was edited by ian42 on Fri 18 Feb 23:26]

 

Replies:

tommieg

68.209.176.106

"Re(1):Troubleshooting questions" , posted Sat 19 Feb 20:25user profileedit/delete messagepost reply


why didnt the tech diagnose and repair the system when he was there?

nona?

 

noname4me3

66.119.33.183

"Re(1):Troubleshooting questions" , posted Sat 19 Feb 01:33user profileedit/delete messagepost reply


If t-stat has a common you might have shorted your wires and blown your transformer. check for voltage at t-stat

 

 

ian42

66.222.88.80

"Re(2):Troubleshooting questions" , posted Sat 19 Feb 09:19user profileedit/delete messagepost reply


which transformer could have blown, rather where can i find it? I check for 24v at the t-stat and got nothing, should i check the leads going into and out of the thansformer? if good should be same on both sides right? thanx for your help!!!

 

 

Xenos
Webmaster



64.230.161.76

"Re(3):Troubleshooting questions" , posted Sat 19 Feb 09:40user profileedit/delete messagepost reply


Your problem will be located in the air handler.