| rabidranger | "383KAV Bryant with fault code 24" , posted Sat 19 Feb 09:24  
Can someone help me with this code? I guess it means "secondary voltage source fuse open". Is it user serviceable?
HELP!! NO HEAT IN HOUSE TODAY!!!!!
Good leaders are scare so I am following myself.
| | Replies:
|
| Xenos Webmaster 
| "Re(1):383KAV Bryant with fault code 24" , posted Sat 19 Feb 09:39  
Look on the control board for a blown fuse. It's just like one's in your car.
Xenos.
The best way to escape a problem is to solve it.
|
| | rabidranger | "Re(2):383KAV Bryant with fault code 24" , posted Sat 19 Feb 10:12  
I have looked for fuses to see if there are any blown, but I cannot find a SINGLE fuse anywhere on the board?
Good leaders are scare so I am following myself.
|
| | Xenos Webmaster 
| "Re(3):383KAV Bryant with fault code 24" , posted Sat 19 Feb 10:51  
There should be a 3 amp push in fuse right by where the wiring harness is. If there is not check for power on the transformer.
Xenos.
The best way to escape a problem is to solve it.
|
| | rabidranger | "Re(4):383KAV Bryant with fault code 24" , posted Sat 19 Feb 19:19  
Found it, it was buried under the wire harness, all is well after a new fuse, thanks for the tip!
Good leaders are scare so I am following myself.
|
| | banff05 | "Re(5):383KAV Bryant with fault code 24" , posted Wed 22 Aug 15:12  
A/C not working thought it was main circut breaker but no i will go home and look for the 3 amp fuse could it be the thermostat?
thanks for any help
rt
|
|
|
|  |
|