ignition isnt working - http://www.hvacmechanic.com/ Forums


Original message

speckfish

66.79.84.88

"ignition isnt working" , posted Mon 24 Oct 19:07user profileedit/delete messagepost reply


i have a heil fuel oil furnace model number nuodo84bfa1ouno84b12a1 and when i try to turn it on the pump runs and i am getting fuel out but the igition isnt working..i have power to it but at the two little progs its not making a spark can you help me

thanks

 


Replies:

Freon

68.220.62.48

"Re(1):ignition isnt working" , posted Mon 24 Oct 20:23user profileedit/delete messagepost reply


Some possibilities are a cracked electrode, weak or dead transformer or improper gapping of the electrode tips. Your choices are replace the transformer first so you know you have adequate high voltage to the electrodes. If still no spark, replace the electrodes. For that task you'll need the oil burner manual that will tell you the correct placement of the electrode tips relative to the nozzle. It might be best to have a service tech come. He may be able to save you a transformer replacement by testing the old one. At least he'll know how to set the electrodes if they need replacing.