Heil blower comes on fine but won't shut off until power interupted. Circuit board in not jumpered for "continuous" blower operation.

Ideas? Any source on-line for a schematic for this board?

Thanks.

Ted

 


Replies:

fitter597

67.165.168.193

"Re(1):Heil VS80" , posted Thu 17 Nov 23:42user profileedit/delete messagepost reply


does the heat work? and is there power to the G terminal on the furnace?

 

 

TedZ

72.139.90.147

"Re(2):Heil VS80" , posted Fri 18 Nov 12:08user profileedit/delete messagepost reply


Thanks for the reply.

Yes heat works and there is power to "G"

Ted

 

 

fitter597

67.165.168.193

"Re(3):Heil VS80" , posted Fri 18 Nov 15:29user profileedit/delete messagepost reply


then thats why the fan runs non-stop, you either have a relay bad in the board holding power on g, or the t-stat is powering g for some reason.

 

 

TedZ

72.139.90.147

"Re(4):Heil VS80" , posted Sun 20 Nov 07:24user profileedit/delete messagepost reply


Thanks. I believe it is a relay. As soon as i get back there i'll check further.

Thanks.

Ted