| TedZ | "Heil VS80" , posted Thu 17 Nov 07:25  
Heil blower comes on fine but won't shut off until power interupted. Circuit board in not jumpered for "continuous" blower operation.
Ideas? Any source on-line for a schematic for this board?
Thanks.
Ted
| | Replies:
|
| fitter597 | "Re(1):Heil VS80" , posted Thu 17 Nov 23:42  
does the heat work? and is there power to the G terminal on the furnace?
|
| | TedZ | "Re(2):Heil VS80" , posted Fri 18 Nov 12:08  
Thanks for the reply.
Yes heat works and there is power to "G"
Ted
|
| | fitter597 | "Re(3):Heil VS80" , posted Fri 18 Nov 15:29  
then thats why the fan runs non-stop, you either have a relay bad in the board holding power on g, or the t-stat is powering g for some reason.
|
| | TedZ | "Re(4):Heil VS80" , posted Sun 20 Nov 07:24  
Thanks. I believe it is a relay. As soon as i get back there i'll check further.
Thanks.
Ted
|
|
|
|