1 stage, 2 stage? - http://www.hvacmechanic.com/ Forums
| Original message
| Replies:
|
| iceman9795 
| "Re(1):1 stage, 2 stage?" , posted Fri 18 Nov 00:57  
not much info to go on there but it sounds like you have a heat pump, on the sub base of your vision pro it has 2 different columns on each side of the terminals one for heat pump and one for conventional, unless you got the wrong stat which is 1 stage heat and cool, which will not work for a heat pump. if you have an orange wire wired up at your stat you have a heat pump, and you will need a stat that is at least 2 stage heat 1 stage cool and heat pump compatable. there are 2 different Vision Pro stats, 1 is 1 stage heat and cool and for gas heat or straight electric heat with air conditioning, the other has up to 3 stages of heat and 2 stages of cooling, you have to set that up in the options in the installer setup. to answer your question if your thermostat is wired up with more than 4 or 5 wires it is multi-stage.
|
| | slopeyjoe | "Re(2):1 stage, 2 stage?" , posted Fri 18 Nov 07:12  
Thanks that helps. I do have the 1 heat/1 cool stat. I will replace it.
|
|
|
|  |
|