| EWG | "HS8 311-9FFP" , posted Tue 14 Aug 21:39  
The compressor finally went bad,can a new 13 seer 2.5 ton condenser be attached to the existing RFC line ?
Ed Gardiser
| | Replies:
|
| rlj1117 | "Re(1):HS8 311-9FFP" , posted Tue 14 Aug 22:12  
no, the rfc line was used as metering device , if the outdoor unit and coil are so old that you are using rfc line , then both outdoor unit and evaporator should be replaced , the new evaporator coil will have the metering device installed , so you will need to replace at least the liquid line and possibly the suction line , hope this helps
|
| static 
| "Re(1):HS8 311-9FFP" , posted Tue 14 Aug 22:04  
Is doing this your idea, or the installer's?
|
| | ewg | "Re(2):HS8 311-9FFP" , posted Tue 14 Aug 22:07  
My idea
Ed Gardiser
|
| | static 
| "Re(3):HS8 311-9FFP" , posted Tue 14 Aug 22:10  
Don't do it. The lineset needs replaced.
|
| | ewg | "Re(4):HS8 311-9FFP" , posted Tue 14 Aug 22:18  
Thanks
Ed Gardiser
|
|
|
|