"HS8 311-9FFP" , posted Tue 14 Aug 21:39user profileedit/delete messagepost reply


The compressor finally went bad,can a new 13 seer 2.5 ton condenser be attached to the existing RFC line ?

Ed Gardiser

 


Replies:

rlj1117

76.4.220.121

"Re(1):HS8 311-9FFP" , posted Tue 14 Aug 22:12user profileedit/delete messagepost reply


no, the rfc line was used as metering device , if the outdoor unit and coil are so old that you are using rfc line , then both outdoor unit and evaporator should be replaced , the new evaporator coil will have the metering device installed , so you will need to replace at least the liquid line and possibly the suction line , hope this helps

 

static



74.140.77.199

"Re(1):HS8 311-9FFP" , posted Tue 14 Aug 22:04user profileedit/delete messagepost reply


Is doing this your idea, or the installer's?

 

 

ewg

75.7.227.28

"Re(2):HS8 311-9FFP" , posted Tue 14 Aug 22:07user profileedit/delete messagepost reply


My idea

Ed Gardiser

 

 

static



74.140.77.199

"Re(3):HS8 311-9FFP" , posted Tue 14 Aug 22:10user profileedit/delete messagepost reply


Don't do it. The lineset needs replaced.

 

 

ewg

75.7.227.28

"Re(4):HS8 311-9FFP" , posted Tue 14 Aug 22:18user profileedit/delete messagepost reply


Thanks

Ed Gardiser