| Jabbmann | "York Diamond 80 Mod # P3huc16L09201A" , posted Thu 16 Aug 01:13:  
I had to replace the blower and when I reinstalled the blower motor I think I may have a wire or two crossed.
When we turn on the air conditioner we hear a sound like water trickling then about 5 seconds later the air comes on & everything works fine.
I have not yet tried the heat, since the weather has been in the 80's and 90's. There is no wiring diagram on the panel. Can you tell me in which order from left to right what color of wires go where on the circuit board?
Thanks
*
[this message was edited by Jabbmann on Thu 16 Aug 01:14] | | Replies:
|
| bubbad 
| "Re(1):York Diamond 80 Mod # P3huc16L09201A" , posted Thu 16 Aug 20:42  
If you had it wired wrong, it probably wouldn't work. A lot of furnaces will delay the blower on for a few seconds after the A/C starts. With the system off, turn the fan switch to on and see how it works.
You should have a heat tap, and a cool tap on the circuit board. depending on your setup, you may have the high speed (black wire)jumpered on both heat and cool. Or black on cool, and maybe blue on heat? Then there is a white wire that is your neutral - that goes with the rest of the 120V neutrals, might say "Circ" on board. Then there are two brown wires that go to your run capacitor.
bubbad
|
| junior1 | "Re(1):York Diamond 80 Mod # P3huc16L09201A" , posted Thu 16 Aug 20:15  
The first thing I would do is see if you can find a numder on the unit to call and see if there is a wiring diagram that can be obtained. There usually is. From there you will have better guidence.
LC
|
|
|
|  |
|