Fan on Condensor Won't Start - http://www.hvacmechanic.com/ Forums


Original message

EGM

68.248.21.98

"Fan on Condensor Won't Start" , posted Thu 16 Aug 12:57:user profileedit/delete messagepost reply


Hello,
My fan on my Carrier condensor won't start unless I tap the top of the unit with a rubber mallet. First I replaced the capacitor. It started for a day, then wouldn't start again. Then I replaced the motor and, again, it started for a day, then wouldn't start again. It still starts if I tap the unit with a rubber mallet. What could the problem be?

What keeps the condensor from starting when the fan doesn't start?

TIA,
EGM

[this message was edited by EGM on Thu 16 Aug 14:57]

 

Replies:

junior1

207.69.137.27

"Re(1):Fan on Condensor Won't Start" , posted Thu 16 Aug 17:12user profileedit/delete messagepost reply


It may be the contactors inside the condenser unit. Most of the time the compressor and the fan are wired in paralle too operate at the same time. Make sure the condenser is leveled. This sometime causes the contactors to work improperly.

LC

 

 

yuri



142.161.78.31

"Re(2):Fan on Condensor Won't Start" , posted Thu 16 Aug 17:31user profileedit/delete messagepost reply


Could be a faulty contactor or poor wiring connections to it. Is the fan blade in good shape, not touching the cowling on the off cycle?

Yuri

 

 

fitter597



67.165.168.193

"Re(3):Fan on Condensor Won't Start" , posted Thu 16 Aug 22:23user profileedit/delete messagepost reply


I'm with Yuri, you need to run new wires and replace the contactor, both cheap fixes

Pipefitters Local 597
" We do it right the first time"

 

 

EGM

68.248.21.98

"Re(4):Fan on Condensor Won't Start" , posted Fri 17 Aug 09:46user profileedit/delete messagepost reply


I replaced the contactor last night and so far, so good.

Thanks for the replies.

EGM