bryant heat pump trips breaker in heat mode - http://www.hvacmechanic.com/ Forums


Original message

esm1071

216.240.101.40

"bryant heat pump trips breaker in heat mode" , posted Wed 12 Dec 18:04user profileedit/delete messagepost reply


I have a bryant heat pump that runs fine in a/c and emrg. heat but trips breaker in heat mode. It will run fine for a while and then trip. At first I thought it was the defrost timer tripping when it would call for defrost - but it happens randomly, with no seemingly specific pattern. Could it still be the defrost timer?

 


Replies:

smythers1968



66.232.220.95

"Re(1):bryant heat pump trips breaker in heat " , posted Wed 12 Dec 18:27user profileedit/delete messagepost reply


Need to have the amps checked while in Heating mode and when there is a call for emergency heat. Heat strips turned on.

Life lesson #12 Know when not to do it yourself.
WOW That Can Hurt!!

 

 

esm1071

216.240.101.40

"Re(2):bryant heat pump trips breaker in heat" , posted Sat 15 Dec 10:09user profileedit/delete messagepost reply


amp draw in heat mode is 7.5 amps and heat strip on in 18 amps. checked for loose wires and other simple things yesterday and still no luck!!!