Carrier 55scx ignition problem - http://www.hvacmechanic.com/ Forums


Original message

jimped

75.168.101.9

"Carrier 58scx ignition problem" , posted Wed 12 Dec 21:50:user profileedit/delete messagepost reply


A few times a day the furnace fails to ignite. When this happens, the blower comes on, ignitor glows a few times, then shuts down. Once I turn the power off and on, it goes through the same cycle. When it's not igniting, I read 30-32 VAC across t1 and t2 on the gas vale. Since this is supposed to be 24v, is a circuit board problem causing this voltage to be too high? Will 5-6 volts over cause the valve to not open? It does click.

Anybody know for sure if I should replace the circuit board or the gas valve? Thanks.

Jim

[this message was edited by jimped on Wed 12 Dec 21:52]

 

Replies:

learner

70.73.177.71

"Re(1):Carrier 58scx ignition problem" , posted Thu 13 Dec 01:41user profileedit/delete messagepost reply


Hi,
Can you tell the voltage reading when furnace is operating normal?

 

 

jimped

206.11.107.34

"Re(2):Carrier 58scx ignition problem" , posted Thu 13 Dec 09:25user profileedit/delete messagepost reply


Usually around 27-28. Seems like it's the same as at startup, then maybe tapers off a few volts. Now this morning, the furnace shut down after running for 5 minutes or so. When I cycled the power, it came on and stayed on until the thermostat told it to shut off.

I'm thinking I'll just try a new circuit board, seem like a good move to the experts?

Thanks.

Jim

 

smythers1968



66.232.220.95

"Re(1):Carrier 58scx ignition problem" , posted Wed 12 Dec 21:53:user profileedit/delete messagepost reply


When it is doing this do you get a flash code?

My thoughts is that you are having a problem with the pressure switch closing

Life lesson #12 Know when not to do it yourself.
WOW That Can Hurt!!

[this message was edited by smythers1968 on Wed 12 Dec 21:56]

 

 

jimped

75.168.101.9

"Re(2):Carrier 58scx ignition problem" , posted Wed 12 Dec 22:42user profileedit/delete messagepost reply


Thanks, but no flash code, there are no status leds on this thing. ces0110057-01 circuit board.

Jim

 

 

static



74.140.76.11

"Re(3):Carrier 58scx ignition problem" , posted Thu 13 Dec 19:44user profileedit/delete messagepost reply


I'd be more inclined to think of a problem with the gas valve then with the circuit board personally.
It's unusual but not unheard of to have more than 30 volts in the control circuit.