"acefurnacefxr - More help please" , posted Wed 12 Dec 23:07user profileedit/delete messagepost reply


acefurnacefxr,
I cleaned out the condensate trap as you suggested and it definitely needed it. Thanks for that information.
Upon further inspection I noticed that water is pooling on the shelf below the inducer fan and motor. It seems to be coming from the condensing heat exchanger. The condensate trap seems to be working properly. This furnace is 15 years old. I can see now that there is no quick fix for this. Is the condensing heat exchanger toast? If so is it worth replacing it? Or could it be a failed seal? Any information would help.

Carrier Weathermaker (1992)
58SXCO60 100 series
Serial #4292A03466
Natural Gas

Thanks again.

 


Replies:

acefurnacefxr



75.13.46.92

"Re(1):acefurnacefxr - More help please" , posted Thu 13 Dec 07:00user profileedit/delete messagepost reply


You may need a new collector box, its the black rectangular box behind the inducer motor. Looks like a big job but in all reality I have changed them in less then an hour . also the 1/2 inch clear round tube that goes from the collector box down to the trap may also be plugged. also there is a smaller (3/8) black hose from the bottom of inducer housing that may also be plugged

HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT

I have been performing HVAC repairs for 23 years

http://www.hillaryclinton.com

 

 

cjp

71.86.194.49

"Re(2):acefurnacefxr - More help please" , posted Thu 13 Dec 08:51user profileedit/delete messagepost reply


Thanks for the reply. It is greatly appreciated