goodman furnace gmnt080-4b 90%efficient..blower motor cycles for 3 to 4 minutes after burner stops.thus blowing cool air at end of cycle...any way to fix of adjust
Thanks dakotakev
| | Replies:
|
| dakotakev | "Re(1):goodman blower motor" , posted Sun 10 Feb 11:46  
thank you jbw and God Bless
Thanks dakotakev
|
| jbwstroker 
| "Re(1):goodman blower motor" , posted Sat 9 Feb 22:37  
There should be a set of dip switches on the furnace control board for the blower "off" delay. You can position these switches to change the amount of time the blower runs after a call for heat ends. 120-150 seconds should be adequate to allow the heat echanger to cool down.