Carrier 58MCA will ignite inconsistantly - http://www.hvacmechanic.com/ Forums
Original message
| sixwongs | "Carrier 58MCA will ignite inconsistantly" , posted Sun 10 Feb 13:24  
I have been having trouble with my 10 year old Carrier 58MCA. It will ignite inconsistantly. I have watched it cycle through and then it would lockout. I have seen the igniter glow to an orange color about 10s seconds later I hear a click 3-4. This cycle happens about 3-4 times before the furnace would shut down. Sometimes after turning the side switch off then on it would start. But lately i have been turning the side switch on 6-7 times before the furnace would ignite. Any suggestions on what to check or replace ?
thanks
sixwongs
| | Replies:
|
| JJRRIC | "Re(1):Carrier 58MCA will ignite inconsistantl" , posted Sun 10 Feb 15:20:  
Check your condensate trap. These have a tendency to clog up after a period of time. And the pressure sw. will open, causing intermittent ignition. Check all your hoses and drain lines. Should be flashing a code 31 if tripping press. sw.Clean flame rod, and make sure no air is getting in undernieth igniter. Check vent differencial. Should be approx. 2.5 on MAGNAHELIC.
[this message was edited by JJRRIC on Sun 10 Feb 15:33] |
|
|
|  |
|