"Goodman" , posted Sun 10 Feb 15:18user profileedit/delete messagepost reply


I have a Goodman GMNT080-4 95% that will not meet temp
and also has ign fail code.
Has new hsi and flame sense. when ignitor lites I here a click on the CKT. board but no gas im getting no voltage at the gas valve after the relay clicks on the board sometimes it works good and sometimes not. and if i set t-stat to 72 it will only make it to about 68 or not work at all unless i reset it I have a Honeywell programmable t-stat had gas pressure checked checked intake and exhaust no problems there.
any help would be great thank you.

 


Replies:

justsomeguy

76.234.23.143

"Re(1):Goodman" , posted Sun 10 Feb 16:14user profileedit/delete messagepost reply


I'd check the vent pressure switch but you probably don't have a magnehelic gauge. i have replaced so many of those switches on that system this heat season that I have lost count.

BillyBob

 

 

bill1

68.41.119.54

"Re(2):Goodman" , posted Sun 10 Feb 16:20user profileedit/delete messagepost reply


Thanks JSG
if i jump it the furnace does the same thing
if i pinch off the hose it shuts the furnace down
so i think its working right i hope
thank you

 

jbwstroker



71.219.223.194

"Re(1):Goodman" , posted Sun 10 Feb 15:25user profileedit/delete messagepost reply


Why were the HSI and FS replaced? Hopefully not just changing parts. Make sure there are no loose or disconnected wires anywhere. Check the connections on the wiring harnesses. If your getting ignitor glow followed by a relay "click" without 24V at the GV terninals, it's probably a bad IFC board assuming all wire connections are good.

"I'd probably be considered an old wise man if I could only remember everything that I've learned".

 

 

bill1

68.41.119.54

"Re(2):Goodman" , posted Sun 10 Feb 16:17user profileedit/delete messagepost reply


Hey JB thanks for the reply
the hsi and flame sense were given to me to try them they are correct. I know that's not way to do things though just thought i would try them.
I just noticed though that with the furnace door off it seems to work fine.
so is it intake air,temp I don't know anymore.
baseball bat might work good at this point.
Thank you

 

 

tom446



66.66.203.58

"Re(3):Goodman" , posted Sun 10 Feb 16:57user profileedit/delete messagepost reply


If it works with burner door off, I'd lean towards blockage in air intake or exhaust pipes, perhaps ice or water. Make sure your exhaust has good pitch back towards the furnace so that water can't lay in it.

If in doubt call a pro !

 

 

bill1

68.41.119.54

"Re(4):Goodman" , posted Sun 10 Feb 17:25user profileedit/delete messagepost reply


Thanks Tom
I am gonna try to run fish tape through both last time I checked they were clean. its three inch all the way 1 90 and two 45s on the exhaust side. intake side is three inch 1 90 1 45 witch I can feel cool air coming in.
I am at wits end. thanks for your help guys.

 

 

tom446



66.66.203.58

"Re(5):Goodman" , posted Sun 10 Feb 17:55user profileedit/delete messagepost reply


While your inducer is running, go outside and listen to your exhaust. A lot of times if there is water in it you can hear it gurguling,

If in doubt call a pro !

 

 

bill1

68.41.119.54

"Re(6):Goodman" , posted Sun 10 Feb 18:24user profileedit/delete messagepost reply


Hey Tom there is some condensation in the trap but its not dripping water. Where does the condensation come from?

 

 

tom446



66.66.203.58

"Re(7):Goodman" , posted Sun 10 Feb 19:14user profileedit/delete messagepost reply


You have a condensing furnace.The condensation is normal, most of it comes from your secondary heat exchanger. This is why there is a condensation drain system built into the furnace. It is normal for the trap to have water in it. However on a yearly basis you should carefully pull the incoming and outgoing hoses on it to make sure they are clean and unobstructed. I pull my trap and clean it annually with white vinager and hot water.

If in doubt call a pro !

 

 

bill1

68.41.119.54

"Re(8):Goodman" , posted Sun 10 Feb 19:55user profileedit/delete messagepost reply


Thanks tom Just pulled the draft motor and tube cleaned
I noticed tom that there is a crack in the black plastic box that the draft inducer screws to. not big but a hairline crack about 6" long.
When i took the motor off behind it in the black box it had about 1/2" of water in it behind a white rubber cap
ran a fish wire through the exhaust pipe no blockage
thanks again tom

 

 

bill1

68.41.119.54

"Re(7):Goodman" , posted Sun 10 Feb 18:57user profileedit/delete messagepost reply


I see a lot of different threads on different sites for this same furnace with the same problems to no avail
Do they have a tech support number.

 

 

mule

24.118.248.124

"Re(8):Goodman" , posted Mon 11 Feb 15:41user profileedit/delete messagepost reply


Remember your P.Sw. is tested twice by board on start up! 1st to make sure its not stuck closed.,then that it does close by ind.motor. It is a N.O. switch.normally open. Test with ohm meter.

"Its only Tin!"

 

 

bill1

68.41.119.54

"Re(9):Goodman" , posted Mon 11 Feb 19:18user profileedit/delete messagepost reply


Thanks mule
I did a test with my meter I have cont when I put vacuum to it
Open when I take it away

 

 

bill1

68.41.119.54

"Re(10):Goodman" , posted Mon 11 Feb 19:20user profileedit/delete messagepost reply


Also I get a real hard light off