Comformaker not working anymore - http://www.hvacmechanic.com/ Forums


Original message

Edrock

75.117.81.40

"Comformaker not working anymore" , posted Mon 3 Mar 22:00user profileedit/delete messagepost reply


I have a Comformaker A/C and gas furnace. Out of the blue it just stop working. Now I currently have no heat and no air. What could the problem be?

 


Replies:

Houston204



98.196.66.53

"Re(1):Comformaker not working anymore" , posted Mon 3 Mar 22:29user profileedit/delete messagepost reply


Does it have a diagnostic light? If so count your flashes and refer to the chart on your panel.

If not, reset power , give it a heat demand and monitor the starting sequence.

If it is a modern gas furnace,
you should hear the induced draft motor run,


see the ignitor glow,


hear the click of your gas valve,


After your flame sensor detects flame


the heat exchanger heats up and the fan starts.

"Tip of the Day" Remember to remove power first.

 

 

Edrock

75.117.81.40

"Re(2):Comformaker not working anymore" , posted Tue 4 Mar 20:58user profileedit/delete messagepost reply


quote:
Does it have a diagnostic light? If so count your flashes and refer to the chart on your panel.If not, reset power , give it a heat demand and monitor the starting sequence.If it is a modern g ...
The unit does not have a diagnostic light. The power was reset to the unit. The unit will not response to a heat nor will it reponse to a A/C demand. When the unit is switch on, and to the heat or A/C position you cannot hear any part the unit running. What do you think?

 

 

Houston204



98.196.66.53

"Re(3):Comformaker not working anymore" , posted Tue 4 Mar 22:20user profileedit/delete messagepost reply


Most furnaces will have a power switch next to them for servicing. I've had cable guy's or other repairmen turn this off thinking it was a light switch.


Measure for power at L1 and L2. If 120VAC is present, measure for 24VAC at R and C.

Is the door switch fully depressed? jumper R(power) to G(fan) to prove your problem isn't your stat.

"Tip of the Day" Remember to remove power first.

 

 

Edrock

75.117.81.40

"Re(4):Comformaker not working anymore" , posted Wed 5 Mar 09:48user profileedit/delete messagepost reply


Would this switch control the furnace in the house and the A/C unit outside the house?

 

 

Edrock

75.117.81.40

"Re(5):Comformaker not working anymore" , posted Sat 8 Mar 14:35user profileedit/delete messagepost reply


Bad switch!!! Thanks to all the brilliant minds for the help.

 

 

cubstakeseries

128.190.62.54

"Re(5):Comformaker not working anymore" , posted Wed 5 Mar 12:52user profileedit/delete messagepost reply


No just the furnace. Looks like a light switch. If you cannot find it reset by taking bottom door off.