Heat pump unit cools/ no heat other than Emrg - http://www.hvacmechanic.com/ Forums


Original message

GeeZer

75.181.22.117

"Heat pump unit cools/ no heat other than Emrg" , posted Wed 5 Mar 07:31user profileedit/delete messagepost reply


I just bought a house with a Payne heat pump. The Amana Thermostat is a mercury type, two stage heat/one cool. In cool mode the outdoor unit runs fine including compressor. In heat mode, only Hi Temp resistive heat works. Air handler cuts on in this mode also. There is 240 volt power to the unit in the heat mode, but compressor/outdoor fan fails to operate. Any ideas, tips?..thanks!

GeeZer

 


Replies:

bigglenn357



72.75.49.197

"Re(1):Heat pump unit cools/ no heat other tha" , posted Thu 6 Mar 06:15user profileedit/delete messagepost reply


Check and see if there is a jumper wire from y to w on back of t-stat,y is your first stage of mechanical heat so when you have a heat call on w the jumper wire will power y without sending power to your reversing valve

Big Glenn
"Imagination is more important than knowledge" (Albert Einstien)

 

cubstakeseries

128.190.62.54

"Re(1):Heat pump unit cools/ no heat other tha" , posted Wed 5 Mar 12:51user profileedit/delete messagepost reply


Check voltage to contactor at outdoor unit. Could be a bad board in the outdoor unit. If there is a board, check voltage going into board first, then coming out of board. If no voltage getting to board, check wiring at indoor unit and tstat. If voltage getting to board, but not out bad board.