"Intertherm blower won't turn on" , posted Thu 6 Mar 18:12user profileedit/delete messagepost reply


My husband replaced our t-stat with a new programmable Honeywell, and the AC works great (calls for air, turns on, blower starts a few seconds later,) but when the t-stat calls for heat, I can hear the furnace turn on, but the blower won't kick on. Any thoughts?

 


Replies:

yuri



207.161.172.96

"Re(1):Intertherm blower won't turn on" , posted Thu 6 Mar 18:33user profileedit/delete messagepost reply


Is it an electric furnace? The old thermostat may have had a switch to turn on the fan simultaneously with the heat. The new tstat may have this switch on the subbase or need to be programmed for use with an electric furnace. Its a good idea to get an electrician or furnace tech to check the elements and wiring annually for safety etc. They may be able to setup the tstat at the same time.

Yuri

 

 

aevolker

71.189.114.55

"Re(2):Intertherm blower won't turn on" , posted Thu 6 Mar 18:41user profileedit/delete messagepost reply


No, it's a gas furnace. Could the old thermostat have had the switch, too, even though it's gas? We'll probably end up calling an HVAC specialist, but we're going to try another thermostat in the meantime....unless there are any other ideas.

 

 

tom446



66.66.203.58

"Re(3):Intertherm blower won't turn on" , posted Thu 6 Mar 19:12user profileedit/delete messagepost reply


You say you hear the furnace turn on or just a cick at the thermostat? Are you hearing an inducer blower starting? Did you actually see the flame light? If the blower is started by a clixs-on or bi-metal switch it will never come on unless the burners light. First thing I'd look at is making sure the thermostat is wired and programmed properly.

If in doubt call a pro !

 

 

aevolker

71.189.114.55

"Re(4):Intertherm blower won't turn on" , posted Thu 6 Mar 19:35:user profileedit/delete messagepost reply


The thermostat is in the hall and the furnace is in our utility area. When I turn the thermostat to heat, a flame symbol pops up on the t-stat, then I hear something going on in the furnace, but the fan/blower never turns on. If I switch to AC, a snowflake comes up on the t-stat, I hear the AC unit turn on, then the blower (which is the same fan for the furnace) starts blowing out cold air. The pilot is lit...we've checked that several times. :) So since the AC works and I do hear the furnace turn on, I assume (stupid, I know) that
A. the t-stat is programmed properly
B. the t-stat IS calling for heat from the furnace

So, my GUESS is that, either

A. somehow the furnace has a wire that isn't connected properly to the blower or that there's a fuse that's blown or a breaker that popped--but I don't even know if the actual furnace has any fuses and/or breakers (the breakers in the electrical box are all good)....
or
B. that for some reason the t-stat has power for the fan via the AC but not the furnace.

[this message was edited by aevolker on Thu 6 Mar 19:37]

 

 

tom446



66.66.203.58

"Re(5):Intertherm blower won't turn on" , posted Thu 6 Mar 19:59user profileedit/delete messagepost reply


Still need to know if the burners are lighting. Also does the fan run if you put the tsat in the fan on position?

If in doubt call a pro !

 

 

aevolker

71.189.114.55

"Re(6):Intertherm blower won't turn on" , posted Thu 6 Mar 20:20user profileedit/delete messagepost reply


The fan does come on when the tstat is in the on position, but the air is not and does not get warm. And now I'm really gonna show my ignorance...but I don't know where the burners are. If they're near the pilot, then no, nothing is glowing/lit, etc. when the heater is turned on, except the pilot

 

 

tom446



66.66.203.58

"Re(7):Intertherm blower won't turn on" , posted Thu 6 Mar 20:38user profileedit/delete messagepost reply


Not sure whats going on without seeing it, but I'm pretty sure that theres something wrong in the t-stat wiring.

If in doubt call a pro !

 

 

aevolker

71.189.114.55

"Re(8):Intertherm blower won't turn on" , posted Thu 6 Mar 21:20user profileedit/delete messagepost reply


I think we got it figured out. We figured out why the burners weren't lighting, but the tstat still didn't turn the blower on. We tried a different tstat and now everything works as it should. Thanks for all the thoughts and ideas!

 

 

heatpumpguy

216.198.139.38

"Re(9):Intertherm blower won't turn on" , posted Fri 7 Mar 10:23user profileedit/delete messagepost reply


check installer set up options
make sure gas furnace selected