batteries in thermostat - http://www.hvacmechanic.com/ Forums


Original message

macdon221

207.161.167.195

"batteries in thermostat" , posted Tue 15 Apr 20:55user profileedit/delete messagepost reply


I have a Lennox G26 furnace. My batroom exhaust fan has a white-rodgers Dual purpose pressure switch attached to activate the funace blower (for outside air intake) when the batroom exhaust fan is switched on. The Low Voltage wires are connected to the R and G terminals of the furnace to activate the blower when the circuit is closed by the pressure switch. It works as adverised. I also have an AC unit attached to the furnace, connected to the low voltage C and Y terminals. It is winter time here, the AC power from the breaker panel and outside switch is turned off. However, when the bath exhaust fan is activated, the funace blower cuts in, (good so far !) I get what seems to be a transformer HUMM in the AC unit. Any advice?
macdon221

This was my original posting. To add, the stat that I have contains batteries and a 4 wire hookup. There is a jumper between the RH and RC connections. The manual for the thermostat says that if batteries are used no common wire from the thermostat to the funace is required. Is the above problem that i am having with my AC a function of dead batteries? What do the batteries do?

macdon221

 


Replies:

vandvmechanical

71.94.21.164

"Re(1):batteries in thermostat" , posted Sat 19 Apr 22:22user profileedit/delete messagepost reply


The batteries actually make the thermostat work. If you wire in a common wire, the batteries would act as a backup to save the program if you lose power for any length of time.

The hum you are hearing is usualy made by the contactor. Most of the time the only way to get rid of the hum is to replace it.

 

fitter597



67.174.0.159

"Re(1):batteries in thermostat" , posted Thu 17 Apr 23:07user profileedit/delete messagepost reply


Problem is the lennox unit is only good for using as a fart fan............. every time someone talks about fart fans and Lennox Ace seems to chime in....LOL might have something to do with ace being full of shit...LOL

Pipefitters Local 597
" We do it right the first time"

 

acefurnacefxr



75.13.32.233

"Re(1):batteries in thermostat" , posted Wed 16 Apr 07:48user profileedit/delete messagepost reply


You have a very unique situation, its highly UNcommon to activate a fart fan in a bath room off of a furnace control board..........I suggest you call your installing contractor with any and all questions about this unique situation.

HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT

I have been performing HVAC repairs for 23 years