| on2wheels | "Rheem heat pump and honeywell stat" , posted Wed 16 Apr 06:41  
I have installed a new 5 ton 13 seer Rheem Package heat pump. My problem is wiring the Honeywell pro th3210d stat. where do install the brown wire and do I need to install a jumper from E to Aux terminal. I have not turned on the power to try the unit yet. I have it wired as: E - no wire Aux - White Y - Yellow G - Green O - No wire L - No Wire R - Red B - Blue C - No Wire -using battery power
Don
| | Replies:
|
| Houston204 
| "Re(1):Rheem heat pump and honeywell stat" , posted Wed 16 Apr 07:23  
Jumper Aux & E, unless you have 20KW and would like to use 10KW for Aux and 10KW for E.
You will not need the brown wire since your stat does not require C.