"Rheem heat pump and honeywell stat" , posted Wed 16 Apr 06:41user profileedit/delete messagepost reply


I have installed a new 5 ton 13 seer Rheem Package heat pump. My problem is wiring the Honeywell pro th3210d stat. where do install the brown wire and do I need to install a jumper from E to Aux terminal. I have not turned on the power to try the unit yet.
I have it wired as:
E - no wire
Aux - White
Y - Yellow
G - Green
O - No wire
L - No Wire
R - Red
B - Blue
C - No Wire -using battery power

Don

 


Replies:

Houston204



98.196.66.53

"Re(1):Rheem heat pump and honeywell stat" , posted Wed 16 Apr 07:23user profileedit/delete messagepost reply


Jumper Aux & E, unless you have 20KW and would like to use 10KW for Aux and 10KW for E.

You will not need the brown wire since your stat does not require C.