| Hey You | "Old York Champion status code" , posted Sat 19 Apr 09:10  
I have an old york unit (I believe it's a Champion) that will not start (heat or cool). Pressing the contactor makes it start, but the control board status LED is flashing twice.
The control board is labeled "York Guard V 031-01298-000." It also has a label "Texas Instruments 6YG-2".
Can anyone tell me what the status code means and can anyone tell me where I can get a list of status codes for that unit?
Thanks.
| | Replies:
|
| TnNATE1412 | "Re(1):Old York Champion status code" , posted Sat 19 Apr 17:03:  
2 Flashes indicates HIGH PRESSURE LOCKOUT. This indicates the the refrigerant pressures have exceeded the safe limit for operation. Dirty air filter?/restricted indoor coil/indoor fan motor shutting down/outdoor fan motor not running, among other things.
To reset the system, turn power OFF to the indoor unit, then power back on. The system should start after 5 minutes following a call from the thermostat, until the system has another failure, to diagnose the problem.
[this message was edited by TnNATE1412 on Sat 19 Apr 17:11] |
| smythers1968 
| "Re(1):Old York Champion status code" , posted Sat 19 Apr 10:12:  
Need Model # please
Life lesson #12 Know when not to do it yourself. WOW That Can Hurt!!
[this message was edited by smythers1968 on Sat 19 Apr 10:13] |
| | Houston204 
| "Re(3):Old York Champion status code" , posted Sat 19 Apr 14:17  
Do you have 24 volt demand supplied to your unit? If not check your float switch, wiring, stat.
Do you have 24 volts to your contactor? If you do, replace your contactor. If you do not, but you do have 24 volt power entering the unit, it is probably your pressure switch.
I will try to look up you trouble code.
"Tip of the Day" Remember to remove power first.
|
| | Hey You | "Re(4):Old York Champion status code" , posted Sat 19 Apr 14:27:  
No 24 volts to the contactor. Sorry, I should have said that in the first place. And yes, 24V to the control card (between Y and B/C correct.) (Would the status LED flash without it?)
[this message was edited by Hey You on Sat 19 Apr 14:49] |
| | Houston204 
| "Re(5):Old York Champion status code" , posted Sat 19 Apr 16:56  
2 = discharge pressure over 400 psig 3 = discharge line temp over 275 F 4 = discharge line temp did not hit 90 F with 1 hour of call for compressor 5 = 2 defrosts in 1 hour 7 = OD Sensor open or shorted 8 = Liquid line sensor open or shorted 9 = Bonnet sensor shorted
"Tip of the Day" Remember to remove power first.
|
| | Houston204 
| "Re(7):Old York Champion status code" , posted Sat 19 Apr 21:08  
That would do it.
You might also verify that your filters clean.
"Tip of the Day" Remember to remove power first.
|
|
|
|  |
|