| barnold | "replacing white-rodgers with Hunter thermosta" , posted Sun 20 Apr 09:55  
I purchased a hunter 44260 to replace my old white-rodgers thermostat. I can't figure out how to label and connect the wires. My wires are as follows: G - Green Y - Yellow O - Orange W2- White E- Brown XI - Blue R - Red
I can figure out the red and green wires using the conversion chart included in the instructions but other than that i'm lost. can you help
Arnold
| | Replies:
|
| barnold | "Re(1):replacing white-rodgers with Hunter the" , posted Tue 22 Apr 03:53  
The old one is 1F58W-72 2 stage heat /1 cool
Arnold
|
| | Houston204 
| "Re(2):replacing white-rodgers with Hunter the" , posted Tue 22 Apr 07:39:  
X1 = C
You must configure your new stat for heatpump operation before it will energize the O terminal with demand for cooling.
Cooling demand at Y with no power to O is stage 1 heat. The factory setting will produce this with heatpumps in cooling demand unless you configure your stat properly.
After configuring option 170 to 7 (multistage heatpump) and setting 190 to 0 (O/B terminal is O) your system should operate correctly.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Tue 22 Apr 21:04] |
| barnold | "Re(1):replacing white-rodgers with Hunter the" , posted Mon 21 Apr 21:05:  
the model number is RTH 7500. When I hooked it up to C the heat came on. Not good here in Florida. Getting hotter.
Arnold
[this message was edited by barnold on Mon 21 Apr 21:28] |
| | Houston204 
| "Re(2):replacing white-rodgers with Hunter the" , posted Mon 21 Apr 21:41  
option 170 = 7 option 190 = 0
You will only get heat with cooling demand unless you configure your new stat for heatpump operation.
Post the number for your old stat. The White Rodgers. I'm still 99% sure X1 = C (common).
"Tip of the Day" Remember to remove power first.
|
| | Houston204 
| "Re(3):replacing white-rodgers with Hunter the" , posted Mon 21 Apr 22:56  
"Tip of the Day" Remember to remove power first.
|
| barnold | "Re(1):replacing white-rodgers with Hunter the" , posted Mon 21 Apr 18:03  
I purchased the Honeywell suggested but there is no indication as to where to connect the X1 wire, can you help? All of the other wires were clearly labled and connected as below with my wire lables listed first: G - G Y - Y O - O/B R - R W2 - AUX E - E X1 - ??
Arnold
|
| | Houston204 
| "Re(2):replacing white-rodgers with Hunter the" , posted Mon 21 Apr 20:29  
If you post the model number for your old stat, I will gladly look it up.
99% sure X1 = C (common)
"Tip of the Day" Remember to remove power first.
|
|
|
|  |
|