"fan stays on" , posted Sun 20 Apr 11:06:user profileedit/delete messagepost reply


We have a 16 year old Trane Weathertron Heat Pump, American Standard Air Handler, and Honeywell PROTH4000 thermostat.

When heating, the fan turned off accordingly in auto mode.

We started the a/c up this week, and now the fan will not turn off in auto mode or even when the thermostat is set to system off. We are unplugging the unit to turn the fan off.

We recently had the thermostat installed professionally (less than 60 days ago) and had the unit serviced less than a month ago.

Thanking you in advance.

[this message was edited by jthompson57 on Sun 20 Apr 11:07]

 

Replies:

turbotommy

207.119.59.135

"Re(1):fan stays on" , posted Wed 23 Apr 07:06user profileedit/delete messagepost reply


I am having the same problem at a job. I even removed the thermostat completly and the fan still runs. I had to on plug the fan in the attic. Please let me know what you find.

Thanks

Tommy turbo
Lake Dallas TX

 

Houston204



98.196.66.53

"Re(1):fan stays on" , posted Sun 20 Apr 12:29user profileedit/delete messagepost reply


The low voltage fuse in your air handler probably needs replacement. It probably looks like this one...



The B terminal on your new stat should not be in use with a Trane or American Standard system. (It is used with Rheem, Ruud, & Weatherking). Blue wires to C (common).





Another possibility is your control wire to the outdoor unit. If Orange is shorted to common or the refrigerant piping it will pop a fuse.

"Tip of the Day" Remember to remove power first.