"Goodman Burp" , posted Mon 21 Apr 16:32user profileedit/delete messagepost reply


Furnace I installed is making "poof" sound and blowing a small amount of air from the front cover about every 2 minutes while running. Problem stops when the front cover is removed.No gas smell, furnace runs as normal.
This symptom began when we moved the exhaust and intake through the roof on a remodel after having a temporary outlet to the side of the house. Exhaust has 2-45s for a 20' vertical rise, intake has 2-90s and 2-45s. Roof outlet is combination intake and exhaust
Furnace is a Goodman GMH95.
My best guess is that it is an fresh air intake problem.

lsw7

 


Replies:

theduke03

24.250.18.179

"Re(1):Goodman Burp" , posted Mon 21 Apr 18:45user profileedit/delete messagepost reply


Disconnect intake at unit and run furnace. If problem goes away then it's the intake pipe. What is the model# of furnace? What size is the flue? Are both intake and exhaust pitched towards furnace on all horizontal sections? Also I'm interested in what your flames are doing so next time watch it when you fire it up and report back

Some of the pictures displayed here are brought to you by Houston204. Be Safe.

 

 

lwolfe7

76.115.3.179

"Re(2):Goodman Burp" , posted Mon 21 Apr 19:32user profileedit/delete messagepost reply


Model #GMH950703
Will try disconnecting intake
2" intake and exhaust.

lsw7

 

 

dwcaveney



69.104.140.120

"Multi-positional Convertable 1-2 stage" , posted Tue 22 Apr 01:28:user profileedit/delete messagepost reply


When you changed the vent direction, what out let option did you use?

Is the furnace installed, discharge right, left, up?

ICBW, but I think the GCH9 is the counterflow version of this furnace, so it is not a down-flow, right?

Re-check page 15 of your install manual.
http://securenet.goodmanmfg.com/pdf/infoPdf/Lit/IO-299A.PDF

DW

[this message was edited by dwcaveney on Tue 22 Apr 01:53]

 

 

lwolfe7

76.115.3.179

"Re(1):Multi-positional Convertable 1-2 stage" , posted Tue 22 Apr 11:18user profileedit/delete messagepost reply


The furnace is in the upflow position (as per pg 15).

The furnace discharge is up.

After checking pg 15 everything I did seems OK.

Thanks for the advice.

lsw7