"Outside Unit wont turn on, unless....." , posted Wed 23 Apr 23:03user profileedit/delete messagepost reply


I push in the contacts on the contactor. If I hold them in, everything seems to run great. But the minute I let go of them, they pop out and everything shuts off. Any ideas? Oh I have a Carrier Weathermaker 8000.. Its approximately 13-14 years old (Just entering its prime!) I replaced the fan about 3 years ago and replaced the capacitator today thinking that might be it.

 


Replies:

Houston204



98.196.66.53

"Re(1):Outside Unit wont turn on, unless....." , posted Wed 23 Apr 23:11user profileedit/delete messagepost reply


Best guess with the limited provided information...

Low pressure switch has locked out due to lack of refrigerant.
Evaporator coil.

Measure for 24 volts entering your condenser. If control voltage is entering your unit but is not present at your contactor, it is probably a pressure switch.





Capacitors will hold a charge for a few minutes after removing power. Be Careful.

"Tip of the Day" Remember to remove power first.

 

 

ckb24

68.227.126.156

"Re(2):Outside Unit wont turn on, unless....." , posted Wed 23 Apr 23:24user profileedit/delete messagepost reply


What more information could you use? I will be happy to supply it! So if I have 24 volts entering the condensor, then I can assume that I need Freon? And do you have any diagrams of the pressure switches? I am handy, but a novice at AC repair..

 

 

Houston204



98.196.66.53

"Re(3):Outside Unit wont turn on, unless....." , posted Wed 23 Apr 23:37:user profileedit/delete messagepost reply


Post your model number. 38TRA048-321 ?
The 3rd and 4th digits of your serial number indicate the year.

My Example shows a 5 minute time delay relay. If your unit is equipt with a timer it could also be the cause.

Is this a heat pump? 38YRA

Follow the voltage, where does it stop? If you have 24 volts to your contactor but it does not pull in, replace youre contactor.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Thu 24 Apr 00:03]

 

 

ckb24

75.33.129.141

"Re(4):Outside Unit wont turn on, unless....." , posted Thu 24 Apr 09:32user profileedit/delete messagepost reply


Model # is 38YC036310

And yes its a heat pump... It was made in 93..

 

 

Houston204



98.196.66.53

"Re(5):Outside Unit wont turn on, unless....." , posted Thu 24 Apr 22:11user profileedit/delete messagepost reply


If you have 24 volts between Y (blue or yellow) and C (brown), but do not have 24 volts between T1 (blue or yellow) and C, it is your pressure switch.

"Tip of the Day" Remember to remove power first.