Trane XL 80-Blower remains on constant - http://www.hvacmechanic.com/ Forums
Original message
| jgsr | "Trane XL 80-Blower remains on constant" , posted Mon 28 Apr 14:22  
My Trane XL 80 continues to blow air (cool) after flame is extinquished. I don't know if this is a unit problem or theremostate problem. Any ideas?
Thanks for your help!
| | Replies:
|
| Zzz | "Re(1):Trane XL 80-Blower remains on constant" , posted Tue 29 Apr 21:48  
There is a set of dip switches on the board that change the fan off timing, get the installation guide and set it to around 100 secs
|
| acefurnacefxr 
| "Re(1):Trane XL 80-Blower remains on constant" , posted Mon 28 Apr 15:29  
Most likely a stuck relay on the main board
HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT
I have been performing HVAC repairs for 23 years