I have two systems installed, both tempstar with out door heatpump... prob seems to be hitting hi limit in airhandler, and fan continously runnin at random and odd times. these are in two seperate locations, and I have tried everything form air flow to circuit board? any help would be greatly appreciated.
j-
| | Replies:
|
| Houston204 
| "Re(1):tempstar heat pump problem" , posted Thu 1 May 20:18  
Verify that your indoor coil, filter and blower wheel are clean. Measure the indoor fan motor amp draw and capacitor microfarad reading.
A static pressure measurement would verify proper airflow.