tempstar heat pump problem - http://www.hvacmechanic.com/ Forums


Original message

northernstar108

206.63.86.71

"tempstar heat pump problem" , posted Thu 1 May 12:00user profileedit/delete messagepost reply


I have two systems installed, both tempstar with out door heatpump... prob seems to be hitting hi limit in airhandler, and fan continously runnin at random and odd times. these are in two seperate locations, and I have tried everything form air flow to circuit board? any help would be greatly appreciated.

j-

 


Replies:

Houston204



98.196.66.53

"Re(1):tempstar heat pump problem" , posted Thu 1 May 20:18user profileedit/delete messagepost reply


Verify that your indoor coil, filter and blower wheel are clean. Measure the indoor fan motor amp draw and capacitor microfarad reading.

A static pressure measurement would verify proper airflow.

"Tip of the Day" Remember to remove power first.