"suction and discharge pressure same" , posted Mon 5 May 08:32user profileedit/delete messagepost reply


After charging my a/c system to data plate specs. for the ambient tempature, the sution pressure was only 10 psig different that the high side and I am wondering what would cause this. no foul odor coming from the system, deep vacuum pulled before charging. comprssor is operating.

ACD

 


Replies:

djgilbert

24.164.88.246

"Re(1):suction and discharge pressure same" , posted Mon 5 May 21:47user profileedit/delete messagepost reply


Just wondering, what was the reason you had to recharge your system?

Don

 

 

acdearin

12.207.182.75

"Re(2):suction and discharge pressure same" , posted Tue 6 May 07:48user profileedit/delete messagepost reply


REPLACED THE ELECTRIC FURNACE WITH A GAS ONE, HAD TO MOVE THE EVAPORATER FOR THE DOWNFLOW FURNACE.

ACD

 

Jojo98

152.86.133.139

"Re(1):suction and discharge pressure same" , posted Mon 5 May 12:47user profileedit/delete messagepost reply


Sounds like you got a busted valve in the compressor.

 

TnNATE1412

24.158.140.10

"Re(1):suction and discharge pressure same" , posted Mon 5 May 10:07user profileedit/delete messagepost reply


Could be a stuck reversing valve or the compressor is bypassing internally. The problem could also be something different, recommend having system checked to verify.

 

 

acdearin

12.207.182.75

"Re(2):suction and discharge pressure same" , posted Mon 5 May 19:05user profileedit/delete messagepost reply


THANKS FOR THE HELP REALLY APPRECIATE IT.