"RUDD Contactors" , posted Tue 6 May 07:12user profileedit/delete messagepost reply


Hello guys, I've got a Rudd heat pump that has a welded up set of contacts and it's causing the outside fan and compressors to run nonstop, electric bill out of control. Problem is the P/N writing has worn off with age on the contactor and there's so many different ones out there I don't know what P/N to search for. My unit model # is "UPGB 049JAZ" 208/230 volt. All that I can make out on the contactor is that it's made by Honeywell and it's a single pole. Can someone help me out with what contactor P/N I need to ask for? Thanks

 


Replies:

Houston204



98.196.66.53

"Re(1):RUDD Contactors" , posted Tue 6 May 07:43user profileedit/delete messagepost reply


Single pole 30 amp contactor with a 24 volt coil.

"Tip of the Day" Remember to remove power first.

 

 

petey48

4.154.34.172

"Re(2):RUDD Contactors" , posted Tue 6 May 18:45:user profileedit/delete messagepost reply


I'm going to use what you told me but I have a question. A maint. guy at work today give me a used 30A 24v coil double pole comtactor and said it would work fine, so I took it as a freeby. I'm no electrician but I do know on the single poll that one side stays hot,and the double pole both side drops out completely breaking the circuit. Is there a reason that one side needs to stay hot? And would the 208/230 24v double pole contactor do in an emergency? I'll keep it just in case. Thanks for your help.

[this message was edited by petey48 on Tue 6 May 20:30]

 

 

Houston204



98.196.66.53

"Re(3):RUDD Contactors" , posted Tue 6 May 19:55user profileedit/delete messagepost reply


I actually prefer 2 pole contactors, unless, I see a crank case heater wired to opposite sides of the leg broken by a single pole contactor.

A 240 volt crank case heater wired this way will only be energized when you do not have a demand from your stat. This lowers your operating cost, increasing efficiency.

I see this done with Carrier condensers.

"Tip of the Day" Remember to remove power first.

 

 

Houston204



98.196.66.53

"Re(4):RUDD Contactors" , posted Tue 6 May 20:34user profileedit/delete messagepost reply





"Tip of the Day" Remember to remove power first.

 

 

petey48

4.154.37.152

"Re(5):RUDD Contactors" , posted Wed 7 May 07:11user profileedit/delete messagepost reply


Thanks Houston204 I'll keep this as a future reference. This tells me what each piece controls.

 

 

Houston204



98.196.66.53

"Re(6):RUDD Contactors" , posted Thu 8 May 21:51user profileedit/delete messagepost reply


My example was a Carrier.

"Tip of the Day" Remember to remove power first.