I have an ICP Tempstar outside unit
MODEL #TCH242AKD1, S/N EO52735309, P/N 328876-4191

AIR HANDLER # EBX4800A

THERMOSTAT IS MULTI-STAGED BRAEBURN MODEL 5200 PROGRAMABLE

It appears to be short cycling, when it runs I have 26vac on both sides of contactor.
If I manually press it in, it runs & cools.
It cycles off before reaching set temp, it only seems to run for about 5 minutes not more than 10 minutes.
When off there is no 26vac on sides of contactor.
I removed low pressure switch contacts from circuit board no joy, I jumpered low pressure switch terminals on circuit board no joy, read out ohms on press sw was about .2 on a fluke 77, read for continuity and it was closed, not infinity.

While it was runing I added enough R-22 to raise low pressure about 4 psi on the low side. OAT was +92 degrees F, starting low pressure was about 45, I don't remember the hi pressure reading!!!

From other posts I'm thinkinking time delay relay or something from the air handler or thermostat

So where do I go from here?

JZHJR

 


Replies:

theduke03

24.250.18.179

"Re(1):ICP Tempstar compressor/condensor short" , posted Thu 8 May 21:33user profileedit/delete messagepost reply


Adding freon is not a troubleshooting technique. You have a switch opening in the low voltage circuit. This can easily be found with voltmeter. Run unit and when it shuts down, check across each switch. The open switch will read 24v. Usually there's only a low pressure switch or high pressure switch or both.
Is there a time delay relay?
Is this a heatpump?
Is 24v still present between Y and C when unit shuts off?
If you don't know what you're doing you should call a pro.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

jzhjr

24.127.230.49

"Re(2):ICP Tempstar compressor/condensor short" , posted Thu 8 May 22:14user profileedit/delete messagepost reply


This is a heat pump, I didn't see a hi press switch.
Not sure if there is a time delay or where the time delay relay would be! It has 2 circuit boards, 1 is a defrost control, not sure what the other is?
It also has a condesate overflow shut-off switch.
I'm planning on taking a vacuum to suck out pipe to make sure its not clogged.

JZHJR

 

 

theduke03

24.250.18.179

"Re(3):ICP Tempstar compressor/condensor short" , posted Thu 8 May 22:16:user profileedit/delete messagepost reply


It's not the overflow switch. It's the defrost board. Refer to post below about having a pro correct the charge.

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Thu 8 May 22:19]

 

 

jzhjr

24.127.230.49

"Re(2):ICP Tempstar compressor/condensor short" , posted Thu 8 May 21:57user profileedit/delete messagepost reply


Thanks I'll check for low voltage opens in the morning, I assumed servicing was low before I began troubleshooting. The unit is only 2 years old, no evidence of leaks.
What I did notice that I was unfamiliar with is that it had an extra set of service fittings above the valved ports? Are most new units equipted like that?
Thanks for your help I'll post my findings tomorrow

JZHJR

 

 

theduke03

24.250.18.179

"Re(3):ICP Tempstar compressor/condensor short" , posted Thu 8 May 22:08:user profileedit/delete messagepost reply


Most heat pumps are. Could be the defrost control board too. If you raised the suction pressure then your system is now overcharged and you can expect premature compressor failure if not corrected and soon. Should be done by pro who can interprate pressures and temp readings. While he's there he can find out the original problem in a minute or two and then you will be good as new.

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Thu 8 May 22:13]

 

 

jzhjr

24.127.230.49

"Re(4):ICP Tempstar compressor/condensor short" , posted Thu 8 May 22:31user profileedit/delete messagepost reply


Should I remove the existing board & take it in for a replacement or would it be enough to just get the part numbers off of it? I'll also take some digital pictures of it!

JZHJR

 

 

theduke03

24.250.18.179

"Re(5):ICP Tempstar compressor/condensor short" , posted Thu 8 May 22:44user profileedit/delete messagepost reply


Do both.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

jzhjr

24.127.230.49

"Re(6):ICP Tempstar compressor/condensor short" , posted Thu 8 May 23:01user profileedit/delete messagepost reply


For correcting the charge the manual suggests using the superheat method, I've normally just used the gauges! I know I dumb assed it by just adding refrigerant, I was in a hurry as this is a rental property!! Now I'll have to go back & do it right. Is the superheat method preferred for newer units?
Again thanks for all your advice.

JZHJR

 

 

theduke03

24.250.18.179

"Re(7):ICP Tempstar compressor/condensor short" , posted Thu 8 May 23:21user profileedit/delete messagepost reply


Whatever the manual says. If it has a txv then you would charge by subcooling.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

jzhjr

24.127.230.49

"Help please! Houston 204 Tempstar short cycle" , posted Fri 9 May 11:40user profileedit/delete messagepost reply


Well I blew out the evaporator tray & line & sucked & vacuumed the outside drain line found some mulch wood chips.
Also reset programmable thermostat.

The unit is now working more normal providing cooling air inside. The condensing unit is cycling on & off at about 15 to 20 minute cycles, while the inside unit never shuts off.
Could it be because it is likely overcharged? Because of my bone head haste!!

I need a new battery for my digital thermometer, which I'm havin problems finding!

Does anyone or Houston 204 still think I need to replace the defrost circuit board? #1087952, CEPL 130547-01 05 27

It also has the other board which appears to be an electronic thermostat, I'm not sure # E61 Thermostat 26-05-004,
Carrier 108897 E61 300000-1

Thanks in advance for you help

JZHJR

 

 

theduke03

24.250.18.179

"Re(1):Help please! Houston 204 Tempstar short" , posted Fri 9 May 18:43user profileedit/delete messagepost reply


This is no guessing game. You must determine where you are losing the 24v and then why. On a call for cooling Y will be energized w/24v from stat. this 24v powers the contactor thus running compressor. If no 24v at contactor then start working backwards till you find the 24v. You have already determined that it is not the pressure switch by jumping it at the board. I have already determined that it's not the float switch. The only thing left is the board. If you are going to be doing service calls you may want to enhance those meter skills.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

jzhjr

63.167.255.152

"Tempstar working now with issues!!" , posted Fri 9 May 22:21user profileedit/delete messagepost reply


Well it operated all day and the inside unit began cycling on & off as if everything was ok, up until about 3 hours ago when the renter called saying she had water puddling up around the return duct & in the garage at the air handler. Turns out I didn't push the condensate safety switch all the way in as its partially obstructed by armaflex from another pipe. Anyway the drain was sucked out with a vacuum again, and while all this was going on a neighbor came by and said he had similar problems & found some spackling globs & pieces of drywall in his & that he used some bleach to disolve it. So at this point my wife tried it cause I'm at work & sure enough she got a bunch of more solids & more mulch chunks out of the drain near the outside unit. So tomorrow I'll pull the panels off the air handler & clean the evaporator coils "A" frame, evaporator tray & drain, Also I'll use coil cleaner on the outside condensor unit then adjust the over charging using the superheat method. It does have a TXV metering device!! The instructions say to remove in 4 to 6 oz. increments, I have a scale for weighing during charge, but I'm not sure how I can calculate discharge because I don't have recovery equipment, only a vacuum pump!!! Any suggestions?
As for the low voltage loss I only don't have it present when the outside unit cuts off. I checked power to the defrost coil when the condensor unit shuts off & still had 26vac.

JZHJR

 

 

Houston204



98.196.66.53

"Re(1):Tempstar working now with issues!!" , posted Sun 11 May 23:26user profileedit/delete messagepost reply


I'd say it's your float switch locking out due to poor drainage.

"Tip of the Day" Remember to remove power first.

 

 

jzhjr

24.127.230.49

"Re(2):Tempstar working now with issues!!" , posted Mon 12 May 00:19user profileedit/delete messagepost reply


I think it was the float switch all along! Yesterday morning I went back & tried to do things right, Cleaned the evap coil, Cond coil both with coil cleaner, again verified a very clean drain pipe, no more junk in it, then closed all back up & ran for about 30 minutes.
Here are my readings:R-22 system with TXV
Inside wet bulb +67 F, Outside condensor inlet dry +91.3,
Low press 72 psig +43 F
High press 215 psig +106 F
High press line temp +91.8 F covered
Low press line temp +66 F under armaflex insulated

Do you think its overcharged?

JZHJR

 

 

Houston204



98.196.66.53

"Re(3):Tempstar working now with issues!!" , posted Mon 12 May 01:02user profileedit/delete messagepost reply


23 superheat and 14 degree subcool. Probably okay. Does the outdoor unit nomenclature list the correct subcool?

I usually see a 9 to 16 degree subcool listed.

"Tip of the Day" Remember to remove power first.

 

 

jzhjr

24.127.230.49

"Re(4):Tempstar working now with issues!!" , posted Mon 12 May 01:53user profileedit/delete messagepost reply


It says at OAT 85 degrees F 20 to 25 Superheat degree F Variator or piston.
At OAT 95 degrees F 10 to 15 Superheat degree F Variator or piston.
It only lists Superheat, no subcooling values!

Thanks so much for your help & Dukes also, I've not adjusted charge before using superheat or subcooling but I'm tryin to learn, just a little skitish still, thanks again

 

 

Houston204



98.196.66.53

"Re(5):Tempstar working now with issues!!" , posted Fri 16 May 19:02user profileedit/delete messagepost reply


What is your temperature drop across the evaporator coil?
You want 18 degrees.

"Tip of the Day" Remember to remove power first.

 

 

jzhjr

200.122.143.48

"Re(6):Tempstar working now with issues!!" , posted Fri 16 May 21:08user profileedit/delete messagepost reply


I had the thermostat set at 77 degrees, wet bulb was 67 degrees, I didn't actually stick a thermometer above evaporator outlet!!