"Trane baystat239 to Honeywell RTH6300B" , posted Tue 13 May 17:44user profileedit/delete messagepost reply


Please Help!

I am replacing my Trane Baystat239 for a Honeywell RTH6300B. These are the settings below.

Trane:

G = Fan
R = 24 Vac
Y = Compressor
W = Aux Heat
O = Reverse Valve Cooling
T = Thermister
X2 = Heat strip
B = Common

Honeywell

G = Fan
R/Rc = 24 Vac
Y = ?
W O/B = ?

I have a Tempstar dual Heatpump/Air Con Unit outside.

Manual says:

Do not connection both O and B if you have a Heat Pump (which I do). Connection O wire to O/B W. Do not use C, X or B.

With the information given I would assume that the following is correct but I don't know what to do with the White (W) unless I am way off on this, or if the others are correct. The Honeywell Thermostat says its for Heat Pump/Air Con so I assume it will work. Can someone please untangle this mystery of mine? Thank you in advance!

Trane Honeywell
G = G
R = R/Rc
Y = Y
W = ?
O = O/B W
T = Not used
B = Not used
X2 = Not used

Keven

 


Replies:

kevenak

68.200.227.227

"Re(1):Trane baystat239 to Honeywell RTH6300B" , posted Tue 13 May 20:33user profileedit/delete messagepost reply


Thanks 'theduke03' and 'Houston204' for the good advice and quick responses? I appreciate it !

Keven

 

theduke03

24.250.18.179

"Re(1):Trane baystat239 to Honeywell RTH6300B" , posted Tue 13 May 18:04user profileedit/delete messagepost reply


That stat will not work for you. You need a 2 stage heat pump thermostat.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

Houston204



98.196.66.53

"Re(2):Trane baystat239 to Honeywell RTH6300B" , posted Tue 13 May 20:20user profileedit/delete messagepost reply


I agree with Duke, your new stat is not compatible with your multistage heat pump.

I recommend a Honeywell RTH7400 or RTH7500.






Set option 170 to 7 and option 190 to 0. Tape off your old T wire.


"Tip of the Day" Remember to remove power first.

 

 

kevenak

68.200.227.227

"Re(3):Trane baystat239 to Honeywell RTH6300B" , posted Wed 14 May 10:19user profileedit/delete messagepost reply


quote:
I agree with Duke, your new stat is not compatible with your multistage heat pump.I recommend a Honeywell RTH7400 or RTH7500. Set option 170 to 7 and option 190 to 0. Tape off you ...
Houston,

Thanks again. I got the RTH7400, coded the options and now works like a charm !

Keven

 

 

armdburg

63.19.164.240

"Re(4):Trane baystat239 to Honeywell RTH6300B" , posted Sun 29 Jun 10:23user profileedit/delete messagepost reply


I'm replacing the same thermostat with a RTH7500. The only thing I can't figure out is where the T wire goes on the new thermostat. Any help?

Don

 

 

kevenak

68.200.227.227

"Re(3):Trane baystat239 to Honeywell RTH6300B" , posted Tue 13 May 20:34user profileedit/delete messagepost reply


quote:
I agree with Duke, your new stat is not compatible with your multistage heat pump.I recommend a Honeywell RTH7400 or RTH7500. Set option 170 to 7 and option 190 to 0. Tape off you ...
Thanks 'theduke03' and 'Houston204' for the good advice and quick responses? I appreciate it !