| jgro461 | "Replacing a Thermostat" , posted Wed 14 May 22:28:  
Just bought a Honeywell non programable Thermostat model number (RTH110B). Well the one I had was a Very old TRANE Model # ( 3AAT80B1A1). Ok here is my problem the Trane had seven wires hooked up to it and the new one only has places for five, this might be a simple problem for some but for me it is not. If there is any help that anyone can give me that would be great. I am not sure what all of the wires on the old one are for so if I just had a wiring diagram for it that would help out some. Thank you for your help. Also should I have went with a programable thermostat or is this going to be fine.
Do it yourself
[this message was edited by jgro461 on Wed 14 May 22:40] | | Replies:
|
| | Houston204 
| "Re(2):Replacing a Thermostat" , posted Thu 15 May 20:08  
Rc & R = red (use provided jumper) O/B = orange G = green Y = yellow Aux & E = white (use a jumper wire) C = blue tape off your old brown wire.
option 170 = 7 option 190 = 0
"Tip of the Day" Remember to remove power first.
|
| jgro461 | "Re(1):Replacing a Thermostat" , posted Wed 14 May 23:35  
Thank you very much for your help will go tomorrow and get the other one.
Do it yourself
|
| | Houston204 
| "Re(2):Replacing a Thermostat" , posted Thu 15 May 00:54  
If X2 and W were jumpered on your old stat, jumper Aux and E on your new stat.
"Tip of the Day" Remember to remove power first.
|
|
|
|  |
|