"unit will not shut off" , posted Thu 15 May 06:11user profileedit/delete messagepost reply


what would make the blowers to keep running after i shut off the a/c? the inside unit keeps running after the a/c is shut off,the outside unit shuts off but the blowers keep going.

 


Replies:

TnNATE1412

24.158.140.10

"Re(1):unit will not shut off" , posted Thu 15 May 22:31user profileedit/delete messagepost reply


Some units run the inside fan for up to 2 minutes after a system call, if longer than that, make sure the fan switch is not in the ON position, otherwise, the blower relay contacts could be stuck. Would need the relay/circuit board replaced, depending on which your unit uses.

 

 

drelix

68.12.237.224

"Re(2):unit will not shut off" , posted Fri 16 May 15:02user profileedit/delete messagepost reply


now would a bad relay/ciruit board cause the burners not to ignite also?

 

 

hellbilly

24.231.185.189

"Re(3):unit will not shut off" , posted Mon 19 May 10:56user profileedit/delete messagepost reply


This sounds very much like how my problem started. I noticed that the blower was running constantly. I got it to stop by turning off the main power to the unit. But, after turning the power back on, the burner would no longer ignite. My blower does go on and off by using the on/auto on the thermostat now but still not getting a flame. Everything seems fine, ignition is glowing bright, exhaust fan humming away but no gas/flame. I'm still working on it.

 

 

theduke03

24.250.18.179

"Re(3):unit will not shut off" , posted Fri 16 May 16:42user profileedit/delete messagepost reply


Do you have a meter? If not you will need to call a pro.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

drelix

68.12.237.224

"Re(4):unit will not shut off" , posted Fri 16 May 20:23user profileedit/delete messagepost reply


yes i have a meter.