Trane 2TWR2 in 1 Outside Unit won't turn on - http://www.hvacmechanic.com/ Forums


Original message

Kime3400

71.158.170.132

"Trane 2TWR2 in 1 Outside Unit won't turn on" , posted Thu 15 May 17:09user profileedit/delete messagepost reply


The attic unit is blowing air, the outside unit will not come on. It is getting power, all breakers have been checked, all connectors have been checked, no ant's or any other kind of bugs are in the electrical area. Did find one of the connectors that was undone, when I reconnected it, it still will not come on, but there is a weird buzzing or humming sound coming from the unit now. It is not a loud sound, you have to get close to hear it. What could be the problem?

 


Replies:

theduke03

24.250.18.179

"Re(1):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 18:33user profileedit/delete messagepost reply


Are you sure the breaker isn't tripped? Is outdoor fan running?

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

kime3400

71.158.170.132

"Re(2):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:03user profileedit/delete messagepost reply


The breaker is not tripped, it's getting juice at the connections, and the outside fan is not on.

 

 

theduke03

24.250.18.179

"Re(3):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:16:user profileedit/delete messagepost reply


Do you have a meter? Check voltage on both sides of contactor and answer me this:
Is there 24v across contactor coil?
Is there 230v from L1 to L2 on contactor?
Is there 230v from T1 to T2 on contactor?

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Thu 15 May 19:36]

 

 

kime3400

71.158.170.132

"Re(4):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:34user profileedit/delete messagepost reply


i will reply tomorrow, hopefully you will be on. thank you for your help, i just have to leave and it will be dark when i return.