Trane 2TWR2 in 1 Outside Unit won't turn on - http://www.hvacmechanic.com/ Forums
| Original message
| Replies:
|
| theduke03 | "Re(1):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 18:33  
Are you sure the breaker isn't tripped? Is outdoor fan running?
"My dad was the most feared furnace fighter in Northern Indiana."
|
| | kime3400 | "Re(2):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:03  
The breaker is not tripped, it's getting juice at the connections, and the outside fan is not on.
|
| | theduke03 | "Re(3):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:16:  
Do you have a meter? Check voltage on both sides of contactor and answer me this: Is there 24v across contactor coil? Is there 230v from L1 to L2 on contactor? Is there 230v from T1 to T2 on contactor?
"My dad was the most feared furnace fighter in Northern Indiana."
[this message was edited by theduke03 on Thu 15 May 19:36] |
| | kime3400 | "Re(4):Trane 2TWR2 in 1 Outside Unit won't tur" , posted Thu 15 May 19:34  
i will reply tomorrow, hopefully you will be on. thank you for your help, i just have to leave and it will be dark when i return.
|
|
|
|  |
|