"no power to unit" , posted Sat 17 May 18:26user profileedit/delete messagepost reply


well I just did a changeout with a new goodman 16 seer heatpump 3 ton with air handler. My problem consists of yesterday I had power at the indoor fan and everything working. I did not have time for the outdoor so I worked on it today. I did not turn the power off to.... the indoor .... i know i goofed ..... now I dont have voltage at the thermostat. the transformer is showing 28 volts i thought if I blew it it wouldnt show voltage I thoughtit was the transformer because of not turning the power off and possibly touching wires on the outdoor unit. Could it be anything else? please help homeowner not too happy!

 


Replies:

Houston204



98.196.66.53

"Re(1):no power to unit" , posted Sat 17 May 18:30user profileedit/delete messagepost reply


low voltage fuse.

"Tip of the Day" Remember to remove power first.

 

 

horty

68.50.120.227

"Re(2):no power to unit" , posted Sat 17 May 18:36user profileedit/delete messagepost reply


what size fuse does it look like a car fuse"?

 

 

Houston204



98.196.66.53

"Re(3):no power to unit" , posted Sun 18 May 21:26user profileedit/delete messagepost reply


Most fancoils have a 5 amp blade type automotive fuse in the circuit board. Replace your fuse with a matching size.

Example...

"Tip of the Day" Remember to remove power first.