no power to unit - http://www.hvacmechanic.com/ Forums
Original message
| horty | "no power to unit" , posted Sat 17 May 18:26  
well I just did a changeout with a new goodman 16 seer heatpump 3 ton with air handler. My problem consists of yesterday I had power at the indoor fan and everything working. I did not have time for the outdoor so I worked on it today. I did not turn the power off to.... the indoor .... i know i goofed ..... now I dont have voltage at the thermostat. the transformer is showing 28 volts i thought if I blew it it wouldnt show voltage I thoughtit was the transformer because of not turning the power off and possibly touching wires on the outdoor unit. Could it be anything else? please help homeowner not too happy!
| | Replies:
|
| Houston204 
| "Re(1):no power to unit" , posted Sat 17 May 18:30  
low voltage fuse.
"Tip of the Day" Remember to remove power first.
|
| | horty | "Re(2):no power to unit" , posted Sat 17 May 18:36  
what size fuse does it look like a car fuse"?
|
| | Houston204 
| "Re(3):no power to unit" , posted Sun 18 May 21:26  
Most fancoils have a 5 amp blade type automotive fuse in the circuit board. Replace your fuse with a matching size.
Example...
"Tip of the Day" Remember to remove power first.
|
|
|
|  |
|