Original message

seano

72.187.8.1

"Air handler cuts out after 2 to 3 minutes" , posted Sun 25 May 01:29user profileedit/delete messagepost reply


I have an old Singer air handler with a White Rodgers digital thermostat the compressor is fairly new and today the blower started cutting out the compressor still runs.

Thanks
Sean

 


Replies:

Houston204



98.196.66.53

"Re(1):Air handler cuts out after 2 to 3 minut" , posted Sun 25 May 20:29user profileedit/delete messagepost reply


Is line voltage still pressent when this occurs?
Does the fan spin freely when power is removed?
If you answered both questions , Yes, you may only need a new capacitor.

"Tip of the Day" Remember to remove power first.

 

 

seano

72.187.8.1

"Re(2):Air handler cuts out after 2 to 3 minut" , posted Sun 25 May 21:07user profileedit/delete messagepost reply


Thanks it was the cap (shorted)
Does this damage the motor at all ?
I got 2 caps from an appliance junkyard (1 needed) and its running now.
I was worried about and old cap being brought up in voltage that quick.
I will buy a new one on Tuesday.
its gone from 91 deg to 87 I can breathe again
Thanks again.

Thanks
Sean