Air handler cuts out after 2 to 3 minutes - http://www.hvacmechanic.com/ Forums
Original message
| seano | "Air handler cuts out after 2 to 3 minutes" , posted Sun 25 May 01:29  
I have an old Singer air handler with a White Rodgers digital thermostat the compressor is fairly new and today the blower started cutting out the compressor still runs.
Thanks Sean
| | Replies:
|
| Houston204 
| "Re(1):Air handler cuts out after 2 to 3 minut" , posted Sun 25 May 20:29  
Is line voltage still pressent when this occurs? Does the fan spin freely when power is removed? If you answered both questions , Yes, you may only need a new capacitor.
"Tip of the Day" Remember to remove power first.
|
| | seano | "Re(2):Air handler cuts out after 2 to 3 minut" , posted Sun 25 May 21:07  
Thanks it was the cap (shorted) Does this damage the motor at all ? I got 2 caps from an appliance junkyard (1 needed) and its running now. I was worried about and old cap being brought up in voltage that quick. I will buy a new one on Tuesday. its gone from 91 deg to 87 I can breathe again Thanks again.
Thanks Sean
|
|
|
|