"A/C service question for noob a/c tech" , posted Sun 25 May 16:45user profileedit/delete messagepost reply


Posted this on the HVACR page by mistake first sorry for the double posting. Hey all, I just put a 3 ton r22 system in a 5 year old high velocity system. The original a/c in the system was a year old and was hit with a snow plow. I reused the existing coil in the air handler as well as the txv as they are matched with the air handler. I am currently getting 55psi on the low side and 160psi on the high side with the ambient conditions being around 22'C and after running it for a little while you can see the coil start to freeze up. I am not familiar with the high velocity systems and am not sure if this is just a matter of adjusting the TXV. The line set was only about 15ft so as far as I am concerned the factory charge should be enough as far as refrigerant goes. I have 14 years as a natural gas service tech but only a couple years experience doing a/c service any help would be appreciated. thanks

14years as a service tech in Ottawa and the valley. www.reliableheating.ca. For furnace manufacturer ratings go to

http://www.consumerreports.org/cro/appliances/heating-cooling-and-air/gas-furnaces/furnaces-repair-history-205/overview/index.htm?resultPageIndex=1&resultIndex=1&searchTerm=furnace

 


Replies:

northernfitter

64.230.95.67

"Re(1):A/C service question for noob a/c tech" , posted Sun 25 May 17:34user profileedit/delete messagepost reply


Got an old friend on the phone finally with much more a/c experience than I and it sounds like its actually low charge after all. The super heat was high and both high side and low side pressures low. I never thought to check the sub cooling will have to go back on Monday and be a little more thorough.

14years as a service tech in Ottawa and the valley. www.reliableheating.ca. For furnace manufacturer ratings go to

http://www.consumerreports.org/cro/appliances/heating-cooling-and-air/gas-furnaces/furnaces-repair-history-205/overview/index.htm?resultPageIndex=1&resultIndex=1&searchTerm=furnace

 

 

Freon

68.214.135.89

"Re(2):A/C service question for noob a/c tech" , posted Mon 26 May 09:24user profileedit/delete messagepost reply


If the system was working before the snow plow, don't touch the TXV. High superheat means the TXV is wide open and there is still not enough R-22 getting to the coil, as you suspected. You should also notice zero subcooling. As you add R-22, at one point the superheat will drop the the TXV set temp... usually 10 to 15 degrees. Then you should notice the subcooling start to increase. Try for ~10 to 20 degrees subcooling. Of course if the condenser mfg has charging instructions, follow those. All of the above assumes a clean indoor coil and new filter.

 

 

dcdraftworks



68.124.177.169

"Re(3):A/C service question for noob a/c tech" , posted Mon 26 May 12:05user profileedit/delete messagepost reply


Fitter,

Duke thinks you're overcharged, so do I. What is the liquid line temperature?

Elmo

 

 

northernfitter

64.230.17.65

"Re(4):A/C service question for noob a/c tech" , posted Mon 26 May 12:47user profileedit/delete messagepost reply


I couldnt take the temp on the liquid line because apparantly the o2 sensor on my tpi is fubared so I couldnt get to the temp setup on it. I am going to the supplier today to get a seperate temp set up and send back my 709 for warranty repairs.

14years as a service tech in Ottawa and the valley.