"Honeywell CT70A issue" , posted Fri 30 May 21:31user profileedit/delete messagepost reply


Hi, I have a HEIL Heat Pump package unit, Model # PYPA48GA1

I changed out the old thermostat with a Honeywell CT70A. In cooling mode, im having aprox 30 second delay before the inside blower kicks in. This is after the compressor/condenser fan starts.

I am posting some before & after thermostat wiring photos. Im sorry the photos are so big.

Thanks in advance, James

Old Thermostat
Photobucket

New Thermostat
Photobucket

 


Replies:

theduke03

24.250.18.179

"Re(1):Honeywell CT70A issue" , posted Fri 30 May 21:50:user profileedit/delete messagepost reply


That may be a time delay built into the heat pump. Are you sure the old stat didn't do the same thing?

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Fri 30 May 21:50]

 

 

Houston204



98.196.66.53

"Re(2):Honeywell CT70A issue" , posted Fri 30 May 22:03:user profileedit/delete messagepost reply


The new stat isn't exactly an upgrade. I recommend a digital stat. (Jumper W2 to E)




"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Fri 30 May 22:12]

 

 

jwko

69.29.35.13

"Re(3):Honeywell CT70A issue" , posted Fri 30 May 23:02user profileedit/delete messagepost reply


No it never did that with the old thermostat.

Jumper from W2 to E did not help.

 

 

Houston204



98.196.66.53

"Re(4):Honeywell CT70A issue" , posted Sat 31 May 11:58user profileedit/delete messagepost reply


The W2 to E jumper only allows emergency heat to operate if it is ever needed. It was not intended to prevent the delay caused by your sequencer.

"Tip of the Day" Remember to remove power first.