"charging" , posted Mon 2 Jun 19:31user profileedit/delete messagepost reply


Has anyone ever had this problem? Four ton 15 Seer Amana split , 50 ft. of proper sized tubing, 20 degree TD. Can add or release 9 pounds of R-22 and pressures ,TD, and amount of condensate water DOES NOT CHANGE. Inside temp can be 70 to 72 degrees yet extremely humid. Any suggestions?

Apollo

 


Replies:

theduke03

24.250.18.179

"Re(1):charging" , posted Mon 2 Jun 20:27user profileedit/delete messagepost reply


Why stop at 9 lbs? Adding freon does not fix air conditioners.
It would be helpful to know the:
Suction pressure
Head pressure
Suction line temp.
Liquid line temp
Outdoor temp
indoor temp

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

Houston204



98.196.66.53

"Re(2):charging" , posted Tue 3 Jun 07:48:user profileedit/delete messagepost reply


Sounds like a return air leak. Measure the return air temp at the grill and at the unit.

Does this unit have fresh air ducted into the return?

As Duke stated, get the subcool and superheat set correctly.

"Tip of the Day" Remember to remove power first.