Can someone assist me in my exactly how I need wire my new T-stat for my heat pump sustem? Here are my current wire connections on the Baystat:
G=green
O=#FFFAF0
X2=black (jumped to W)
B=blue
F=nothing
U=nothing
W=white (jumoped to X2)
R=red
T=brown
Y=yellow
Please assist in any ideas that you have. Thanks so much.

"Living the dream baby living the dream!"

 


Replies:

Houston204



98.196.66.53

"Re(1):Diag for Baystat 239 to Honeywell Vis P" , posted Tue 3 Jun 18:52:user profileedit/delete messagepost reply


I hope you have the Visionpro TH8320 or the TH8321. The TH8110 is not compatible with your multistage heat pump.

New terminal = wire
G = green
O/B = orange
E = black
C = blue
Aux = white (you can jumper this to E to match the old setup)
Rc & R = red
Y = yellow
Tape off your brown wire. Your new thermostat does not require an outdoor thermister for proper operation.

You must also configure this stat to match your system.
option 170 = 7
option 190 = 0
option 240 = 9 if you have electric auxillary heat








"Tip of the Day" Remember to remove power first.