Electric heater will not turn off - http://www.hvacmechanic.com/ Forums


Original message

mjpogue

71.163.237.219

"Electric heater will not turn off" , posted Wed 4 Jun 00:10user profileedit/delete messagepost reply


My electric heater in my unit will not turn off (i.e it counter acts my a/c). When I disconnecected my W wire for the heater and I can feel my a/c. Does anyone know how to fix my heater problem???

Michael

 


Replies:

theduke03

24.250.18.179

"Re(1):Electric heater will not turn off" , posted Wed 4 Jun 00:28user profileedit/delete messagepost reply


Turn on a/c. Go to the outdoor unit. Check for 24v between W and C. If 24v then disconnect W and see if 24v is coming from the control, or from the W wire. If it's from the control then replace the control and defrost sensor. If it's from the wire then it's a short elsewhere.

"My dad was the most feared furnace fighter in Northern Indiana."

 

Houston204



98.196.66.53

"Re(1):Electric heater will not turn off" , posted Wed 4 Jun 00:25user profileedit/delete messagepost reply


Where did you disconnect it? The stat, sequencer, or circuit board. If it was at the air handler, try disconnecting it at only the stat. If this corrects the problem, replace your stat.

If the problem persists, you may have a damaged stat wire.

"Tip of the Day" Remember to remove power first.