Totaline P474-1050 goes blank when A/C starts - http://www.hvacmechanic.com/ Forums
Original message
| yanng | "Totaline P474-1050 goes blank when A/C starts" , posted Sat 7 Jun 11:50  
I bought a Totaline P464-1050 and connected it to a Climate Master Heat Pump. G to G Y1 to Y1 R to R W1 to O/W1 and I connected the provide resistor between W1 and C on the heat pump. I also switched Heat Pump to ON in step 3 of the advanced setup. The A/C turns on but the display still goes blank and the A/C stays on until I turn the power off from the fuse panel. Is there something I did wrong? Please advise. Thank you in advance for your help.
Yann
| | Replies:
|
| Houston204 
| "Re(1):Totaline P474-1050 goes blank when A/C" , posted Sat 7 Jun 12:37:  
Do you have more conductors coming out of the wall?
Power stealing stats are unreliable. If you do not have at least 5 conductors available, I recommend a Honeywell RTH7400. It can use batteries if common is not available.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Sat 7 Jun 12:51] |
| | yanng | "Re(2):Totaline P474-1050 goes blank when A/C" , posted Sat 7 Jun 19:35  
I finally found another conductor out the wall. I connected it to C on the stat and to C on the heat pump. And I removed the resistor. That works. Thanks for your help.
Yann
|
|
|
|  |
|