"Totaline P474-1050 goes blank when A/C starts" , posted Sat 7 Jun 11:50user profileedit/delete messagepost reply


I bought a Totaline P464-1050 and connected it to a Climate Master Heat Pump.
G to G
Y1 to Y1
R to R
W1 to O/W1
and I connected the provide resistor between W1 and C on the heat pump.
I also switched Heat Pump to ON in step 3 of the advanced setup.
The A/C turns on but the display still goes blank and the A/C stays on until I turn the power off from the fuse panel.
Is there something I did wrong? Please advise.
Thank you in advance for your help.

Yann

 


Replies:

Houston204



98.196.66.53

"Re(1):Totaline P474-1050 goes blank when A/C" , posted Sat 7 Jun 12:37:user profileedit/delete messagepost reply


Do you have more conductors coming out of the wall?

Power stealing stats are unreliable. If you do not have at least 5 conductors available, I recommend a Honeywell RTH7400.
It can use batteries if common is not available.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Sat 7 Jun 12:51]

 

 

yanng

207.244.174.72

"Re(2):Totaline P474-1050 goes blank when A/C" , posted Sat 7 Jun 19:35user profileedit/delete messagepost reply


I finally found another conductor out the wall. I connected it to C on the stat and to C on the heat pump. And I removed the resistor.
That works.
Thanks for your help.

Yann