| challenger | "2 stage amana asx-cond. 1 stage furnace wire" , posted Sat 7 Jun 21:03  
i have a amana asx 4 ton condensing unit with 2 stage copeland scroll compressor. the furnace is a hallmark lbd115 oil with a zettler fan center. the furnace is set up only to use 1 stage cooling. does anyone know if you can wire the condensing unit to operate in a single stage. if so should it be wired to operate y1 or y2?
| | Replies:
|
| Houston204 
| "Re(1):2 stage amana asx-cond. 1 stage furnac" , posted Sat 7 Jun 21:28  
If you only want 1 stage it should be Y2 (jumper Y1 to Y2)
Why don't you run a lower blower speed with Y1 and a higher speed with Y2?
"Tip of the Day" Remember to remove power first.
|
| | CHALLENGER | "Re(2):2 stage amana asx-cond. 1 stage furnac" , posted Sat 7 Jun 21:40  
THE OIL FURNACE HAS A ZETLER FAN CENTER WITH ONLY A Y TERMINAL CONNECTED TO THE FAN MOTOR. ITS NOT A CONVENTIONAL LOW VOLTAGE WIRING TERMINATION BOARD WITH 2 STAGE OPTIONS Y1 AND Y2
|
| | Houston204 
| "Re(3):2 stage amana asx-cond. 1 stage furnac" , posted Sun 8 Jun 01:45:  
If it has a 3 speed fan motor, I'm confident that I could utilize more than one speed with the addition of a relay. It would not, however, be as good as a variable speed furnace.
It seems that I have upset you since you choose to use all capitals, so I'll leave you to your single speed.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Sun 8 Jun 01:52] |
| | CHALLENGER | "Re(4):2 stage amana asx-cond. 1 stage furnac" , posted Sun 8 Jun 08:41  
|
| | CHALLENGER | "Re(5):2 stage amana asx-cond. 1 stage furnac" , posted Sun 8 Jun 08:45  
I THANK YOU AND WELCOME ALL ADVICE. I AM TYPING ALL CAPS BECAUSE IT JUST MAKES EASIER TYPING FOR ME.DO YOU KNOW OF ANY OTHER FAN CENTER THAT YOU CAN SET UP A Y1 AND Y2 TO A DIFFERENT FAN SPEED. THE FAN IS A DIRECT DRIVE 3SPD.
|
| | dwcaveney 
| "Re(6):2 stage amana asx-cond. 1 stage furnac" , posted Sun 8 Jun 17:06:  
1.28.86 all capital srb seals
[this message was edited by dwcaveney on Sun 8 Jun 20:08] |
| | theduke03 | "Re(6):2 stage amana asx-cond. 1 stage furnac" , posted Sun 8 Jun 08:57  
THAT'S NO WAY TO GET A RESPONSE. EASY FOR YOU, PAINFUL FOR US.
"My dad was the most feared furnace fighter in Northern Indiana."
|
| | Houston204 
| "Re(7):2 stage amana asx-cond. 1 stage furnac" , posted Mon 9 Jun 23:28  
Add a relay which interrupts the circuit to High speed. Wire the new relay normally closed to Medium speed. Wire Y2 to the coil of the new relay to initiate High speed.
"Tip of the Day" Remember to remove power first.
|
| | challenger | "Re(8):2 stage amana asx-cond. 1 stage furnac" , posted Wed 11 Jun 13:04  