ok on a newer 13 seer rheem heat pump condenser how does the low voltage wiring go?


yellow-is for the contacter
brown - common
orange-i think it is for the reversing valve?
blue-?
red?

 


Replies:

theduke03

24.250.18.179

"Re(1):rheem heat pump low voltage wiring" , posted Sun 8 Jun 17:46user profileedit/delete messagepost reply


The colors mean nothing. What is imortant is the terminals that said colors are connected to. Having read your previous post I would believe it's wired correctly if it ever worked. Your problem is either a short in the wiring or a shorted component. You will continue to blow transformers until the short is found and fixed. With indoor unit OFF measure ohms across the contactor coil and across the 2 reversing valve wires.
Consider adding a 3amp automotive type fuse to the R wire from transformer to prevent blowing another one.
Post results.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

Houston204



98.196.66.53

"Re(2):rheem heat pump low voltage wiring" , posted Mon 9 Jun 08:19:user profileedit/delete messagepost reply


Rheem will normally use blue for the reversing valve (energize to heat).

So standard color codes would be...
B= blue
R= 24VAC=Red
C= brown
W= white
Y= yellow
G = green (not used outside)

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Mon 9 Jun 08:21]

 

 

allen1980

71.164.56.5

"Re(2):rheem heat pump low voltage wiring" , posted Sun 8 Jun 17:53user profileedit/delete messagepost reply


also on the rheem it isnt hooked up yet this is my first rheem job.lol.

 

 

allen1980

71.164.56.5

"Re(2):rheem heat pump low voltage wiring" , posted Sun 8 Jun 17:52:user profileedit/delete messagepost reply


no i am sorry this was two seperate units i was asking about.but as far as the blown transformer goes is it possible that it is in a sequencer?

[this message was edited by allen1980 on Sun 8 Jun 17:54]

 

 

theduke03

24.250.18.179

"Re(3):rheem heat pump low voltage wiring" , posted Sun 8 Jun 18:20user profileedit/delete messagepost reply


Sure could be a sequencer. Check ohms across the heater( bottom terminals on either side). Compare ohm reading to other sequencers.